Q&A
Compressing Fiberglass
Batts
Q.
I’ve heard that if
you use 5 1/2-inch-thick fiberglass batts in a 2x4 wall, the
insulation will have a higher R-value than standard 3 1/2-inch
batts provide. But some people say that compressing fiberglass
batts lowers the R-value. What’s the story?
A.
Bruce Harley, an energy
efficiency expert at Conservation Services Group,
responds: Both statements are correct. When you compress
fiberglass insulation, you increase its R-value per inch, up to
a point. However, when you compress a batt of a particular
thickness, the total R-value does decrease. For example,
standard low-density batts, at their nominal rated thickness
— R-11 at 3 1/2 inches, or R-19 at 6 inches —
have an R-value of about 3.1 per inch. If you compress a 6-inch
R-19 batt into a 3 1/2-inch cavity, you get about R-14, or 4.0
per inch. This is a much higher R-value per inch, but the total
value of R-14 is still substantially less than the R-19 you
started with. Even in a 5 1/2-inch wall, the R-19 (which is
rated at 6 inches of thickness) gives you only R-18.
For the best performance, any batt should be installed
carefully, to fill the entire space without compressing around
wires, pipes, bridging, or other obstructions. For those
seeking higher R-values per inch than standard fiberglass
batts, one alternative to compressing large batts into small
cavities is to use so-called high-density batts (R-13 or R-15
at 3 1/2 inches, or R-21 at 5 1/2 inches). Although they cost
more than standard batts, they are stiffer, easier to fluff up,
and easier to cut around obstructions in wall framing. These
factors result in a bigger benefit in real-world performance
than the factory ratings indicate.