A.Dave Yates, a plumbing
contractor in York, Pa., responds: The
placement of the tank and check valve are fine;
that ticking sound you hear is coming from thermal
stress taking place in the expansion tank as it
accepts expanding water.
This problem is likely to be more noticeable
during the heating season because that's when there
is the greatest difference between inlet and
storage temperatures: The greater this difference,
the larger the volume that the TXT (a thermal
expansion tank rated for 150-psi maximum working
pressure and potable water) must accept.
For example, if your customers' incoming water
temperature is 40°F (a typical wintertime
temperature for most of the country) and the
storage temperature is set at 140°F, their
50-gallon water heater will generate as much as .75
gallon of thermal expansion.
A 2-gallon TXT that's been precharged to match
an average incoming water pressure of 70 psi would
reach a pressure of 112 psi in this case, but
pressure spikes in municipal systems and
temperature spikes in storage tanks aren't
uncommon, so the actual pressure may be even higher
(For more on the relationship between temperature
and pressure in a domestic hot-water system, see
Q&A, 3/06).
To reduce the noise level, you'll need to reduce
stress on the tank, its bladder, and the potable
water distribution system by increasing the size of
the TXT.
Under the same conditions as the example above,
the pressure inside a larger 4.5 TXT would be 84
psi, which would allow plenty of extra capacity for
spikes in the water system's temperature and
pressure.
Spending a few dollars more on the larger
expansion tank should solve the problem.