To build long-lasting, energy-efficient, healthy houses in
the Florida peninsula and Gulf Coast regions of the United
States, builders must take into account the unique climatic
conditions of the area. Code guidelines are not always helpful,
since the CABO One & Two Family Dwelling Code and the Model
Energy Code are mostly written for heating climates and
advocate construction practices that often are the opposite of
what should be done in cooling climates.
In the summertime along the Gulf Coast and Florida, the
outside air is hot and moisture-laden, so most homes are air
conditioned (see Figure 1).
Figure
1. Moisture control practices for hot, humid climates
(shaded area) are almost the exact opposite of recommended
building practices for cold climates, because moisture is more
likely to enter wall cavities from outside than from
inside.
Under these conditions, code-approved building practices
such as ventilated crawlspaces or the use of vapor diffusion
retarders on the interior side of exterior walls can be
disastrous. In this article, I’ll focus on the
moisture-control techniques my company has learned during 18
years of building and designing homes in hot, humid Texas.
Concrete Slab Foundations
The soil is a constant source of moisture, so we use a sturdy
vapor barrier such as 6-mil poly or visqueen beneath slabs to
prevent ground-based moisture from migrating up through the
concrete by capillary action or diffusion. We lap the joints
liberally and use tape on any tears and around pipe
penetrations. We also use a minimum 11/2-inch sand base under
the slab to further reduce water problems (see "Sub-Slab Vapor
Barriers," 5/94). In addition, the poly helps reduce mineral
efflorescence on the slab surface, a common cause of
discoloration on stained and patterned concrete floors.
Unvented Crawlspaces
Despite what the code books say, in our geographical area I
strongly recommend against ventilating crawlspaces unless I
suspect there is an underground water source beneath the
foundation. If you think about the goal — keeping the
crawlspace dry and inhospitable to mold — the last thing
you want is to encourage the infiltration of warm, moist air
into a cool, dark space. This would lead to condensation on all
crawlspace surfaces, making them vulnerable to decay.
We do not specify vents for crawlspaces, and we make any
access doors fit snugly. We also recommend carefully installing
a 6-mil poly vapor diffusion retarder over the entire dirt
floor. Spreading a few inches of gravel over the poly helps to
keep it in place and protects it from damage. A sealed
crawlspace also stays warmer on the few cold winter days we
have here, minimizing the chance that warm, moist household air
will create a problem when it finds a condensing surface within
the crawlspace.
With a sealed crawlspace, it is imperative that standing
water be kept out. This means that the finish grade must slope
away from the building at a minimum of 1/4 inch per foot. Avoid
sites where the seasonal water table is above the elevation of
the crawlspace.
Wall and Framing System
In the hot, humid South, by contrast to other areas of the
nation, we cool our houses and buildings more than we heat
them. Because the warm outside air usually has more moisture in
it than cool inside air, moisture most often migrates from the
outside of the structure to the inside. If you have a vapor
diffusion retarder on the underside of the gypboard (a common
detail in cold climates), or an impermeable vinyl wall covering
over the gypboard, there is a good chance that warm, moist
outside air migrating through the wall system will condense
once it hits the relatively cool gypboard. This trapped
moisture not only reduces the thermal performance of the wall
insulation; it creates potential problems in the wall cavity
— from unhealthy mold and mildew to structural wood
decay.
Contrary to code, do not use a vapor diffusion retarder on
the interior of the wall system, because walls in the hot,
humid South dry to the inside, not to the outside. Especially
avoid placing a sheet of poly under the gypboard, or covering
the gypboard with vinyl wall-paper. The only place where we use
poly is on the interior side of walls around tub and shower
enclosures that do not abut an outside wall. In these localized
areas, we feel it’s prudent to protect the partition wall
cavity from the high humidity generated in the bathroom.
Exterior sealing.
Houses in humid cooling climates do need to be sealed on the
exterior, but careful detailing is critical. I am wary of
tightly sealed exterior cladding systems, such as synthetic
stucco, that are applied over impermeable rigid foam
sheathings. These stucco systems are never perfect, and rain
water eventually penetrates through cracks around windows and
doors. Even when the foam is well taped or covered with
housewrap or building paper, the surface is often accidentally
punctured during installation, allowing rain water and water
vapor to penetrate the foam and eventually find its way into
the walls.
Whether a building is clad with stone, brick, traditional
stucco, wood, or synthetic siding, we prefer to use plywood or
OSB sheathing covered with 30-pound building paper and a layer
of heat-reflecting foil. This provides a sturdy drainage plane
behind the cladding that sheds water down and away from the
wall cavity (Figure 2).
Drainage Plane Detail
Figure
2. For exterior sheathing, the author prefers to use
plywood or OSB rather than rigid foam. A carefully lapped and
tightly sealed layer of 30-pound building paper over the
sheathing creates a drainage plane that directs water down and
away from the wall. In addition, all cracks and wall
penetrations are sealed on both sides using expanding foam and
caulk.
Where the exterior cladding stands away from the wall, as
with masonry veneers, use weep holes and flexible "moist-top"
flashing at the base to direct water out of the cavity.
Use common sense when installing sidewall flashing and
housewrap or building paper. Because water drains downward,
always lap the uppermost layers of flashing or housewrap over
lower layers (see "Making Walls Watertight," 12/95). Finally,
provide ample roof overhangs: They not only shade windows and
walls, but they help keep rain water off as well.
Infiltration control.
To create a barrier to airflow, seal all holes, cracks, and
other penetrations through walls, ceilings, and floors after
framing is complete, then again after the drywall work is done.
Use expanding foam and a good-quality caulk to seal around
window and door frames. I also insist on using foam-rubber or
neoprene gaskets under all electrical switch and outlet plates
mounted in exterior walls.
At the joint between wall plates and the foundation, I find
that using a continuous roll of foam sill sealer does a better
job of sealing than simply caulking the joint. In our
experience, concrete tends to reject the caulk over time.