Roof Systems
In our area, attic spaces can heat up to 130°F or more
on a hot summer day. Eventually, that heat transfers through
the ceiling insulation into living spaces below, increasing the
cooling load. To counter this problem, we not only suggest
twice as much roof ventilation as most codes recommend, but we
also use a radiant barrier, such as Insul Foil (Advanced Foil
Systems, 820 S. Rockerfeller Suite A, Ontario, CA 91761;
909/390-5125) to keep the attics cool. You can also use
Kool-Ply (Louisiana-Pacific, 111 S.W. Fifth Ave., Portland, OR
97204; 800/299-0028), a labor-saving roof sheathing with foil
laminated directly to it. The radiant barrier blocks the
transfer of heat from the hot roof to the attic. Apply the
radiant barrier to the underside of the roof, not on the attic
floor, and make sure to cut open the radiant barrier along the
ridge and below the low-profile vents so that attic air can
exhaust (Figure 3).
Figure
3. Foil radiant barriers can reduce unwanted heat gain
by up to 40%. The foil barrier should be installed on the
underside of the sheathing and should be cut at the ridge vent
to allow heated air in the attic to escape.Roof Ventilation Details
Figure
4. The author recommends doubling the net ventilation
area in both attics and vaulted roofs. He prefers passive
venting to power vents, which may draw conditioned air out of
the living space.
Where this can’t be done with continuous ridge
venting, such as on hipped roofs, I supplement the ridge
venting with low-profile vents on the roof itself. These should
be located on the side of the roof opposite the direction of
prevailing summer breezes. Don’t substitute power attic
vents for the passive venting techniques just described. They
not only consume power, but often draw conditioned air from the
living space by depressurizing the attic.
Duct Sealing
Mechanical air distribution systems, including ducts and air
handlers, must be installed with minimum air leaks. Otherwise,
a vacuum can occur in the living space, creating an imbalance
that will draw in moist outside air. Consider this
scenario:
The air handler is pulling air from the house through a
short return air duct or well-sealed chase. But because not all
the supply-duct joints and seams are equally well sealed, not
all of that air gets delivered back into the living areas of
the house. Rather, it gets lost to the attic or someplace other
than the building’s occupied zone, creating a negative
air pressure, or vacuum, in the conditioned zone. As a result,
moisture-laden outside air from the attic — or worse yet,
moist and chemically laden air (from insecticides and rat
poisons) from the crawlspace — is drawn into the house
through cracks and poorly sealed pipe penetrations.
To eliminate the imbalance that creates this negative air
pressure, we seal all duct joints and transitions with fibrous
mastic rather than duct tape (Figure 5).
Figure
5. Properly sealing ductwork with mastic will prevent
hvac systems from creating negative pressure in conditioned
living space, which could draw unwanted moisture from the
outside.
We use Versa Grip (Hardcast, P.O. Box 1239, Wylie, TX 75098;
800/527-7092) or RCD #7 Mastic (RCD Corp., P.O. Box 1020,
Eustis, FL 32727; 800/854-7494). Sealing ducts this way is
important both to maintain indoor air quality and to minimize
moisture and mildew. I even suggest setting up the hvac system
to provide slightly positive pressure in the house. This can be
done in a controlled way via a small outside-air intake duct to
the return-air chamber of the air handler. It will provide
outside makeup air and create a positive pressure difference
between the inside and outside. Positively pressurizing the
interior also keeps unwanted moisture from infiltrating the
living environment. In addition, this outside air is
dehumidified by the air handler before it reaches the
home’s interior.
Educate the Homeowner
Using a little common sense, homeowners can keep humidity
levels down inside the house, which will decrease the chance of
molds and mildew growth during the summer and minimize
condensation on windowsills during the winter. Builders can
help by explaining why clothes dryers and kitchen exhaust fans
must be vented directly to the outside, and by providing
bathroom fans with timer switches so the owners won’t
have to remember to turn them off.
Homeowners will "buy into" these preventive techniques if
you explain how they will prolong not just the hidden
structural elements, but the interior paint job, windows,
drywall, and other finishes as well.
Peter L. Pfeiffer, AIA, is a principal in Barley &
Pfeiffer, an Austin, Texas, architectural firm specializing in
sustainable architecture, planning, and energy
consulting.