A.Peitsa Hirvonen, a
licensed electrical contractor and the owner of
SESCO Electrical Inc. in Berkeley, Calif.,
responds: Generally speaking, if an electrical
circuit was properly wired and up to code when it
was first installed, then it's up to code now. Most
inspectors will not make you change out existing
wiring if it appears to be sound and correctly
wired and has not been modified or added to in an
illegal way. But when a contractor completely opens
the walls, floors, or ceilings and makes it easy to
access the wiring, most inspectors will require
those areas to be rewired to meet current code.
The problem, of course, with a two-wire circuit
is that it's not grounded. The old Romex (NM) and
BX (AC) cables had no separate grounding conductor,
or the conductor was so small (16 or 18 AWG) that
it wouldn't count by today's code. This type of
cable can usually be identified by the sheathing,
which looks like snake skin or tarred cloth.
However, there is some old two-wire Romex out there
that looks like the modern plastic/vinyl sheathed
kind, so don't automatically assume there is a
grounding wire. Open the box and check.
In the case of old steel-clad armored cable
(BX), it's still legal to use the metal shield as a
ground, but I wouldn't do it. If you must, make
sure the BX connector has a screw or some type of
clamp that really bites into the metal of the
shield, and that the connector is very securely
tightened against the side of a metal box with the
lock ring. The grounding path could fail if any one
of these connections is not absolutely secure. If
the two-wire circuit happens to be in a conduit
(rigid or EMT), you may use the conduit as a
grounding path, provided all of the connectors and
couplings are tight. Still, I prefer not to rely on
the conduit, and instead always pull a separate,
appropriately sized green grounding conductor.
There are a couple of ways to deal with two-wire
Romex or knob and tube. It's legal to exchange a
two-prong receptacle for a GFCI receptacle or to
put the whole circuit behind a GFCI breaker.
However, you may not be able to get the GFCI
breaker to hold, because old circuits tend to have
some ground leaking. The GFCI protection is
actually much better at preventing electrocution
than grounding is, though you will be required to
mark every outlet with the words "no grounding
conductor present." This is to remind people not to
plug a surge protector into that circuit, because a
surge protector won't work unless it's properly
grounded.
It is possible to upgrade a circuit by running a
separate grounding conductor to the nearest panel,
the service main, or the system grounding
electrode. This would make sense only if the
circuit you were upgrading was close to the
grounding electrode and far from any panels,
including the main. In the time it takes to run a
grounding wire to a panel, you could just as easily
run a new cable with a grounding wire in it.
By the way, it used to be considered okay to run
a grounding wire to the nearest cold-water pipe,
and I've seen them run to cast-iron drain pipes,
gas pipes, metal ducts, and driven ground rods.
Please don't do any of those things! Pipes and
ducts present a real hazard when energized without
clearing the fault, and dirt is a high-impedance
grounding path.
In the end, the best and often the fastest way
to bring a two-wire circuit to code is simply to
rewire it. When that's not possible, your inspector
may accept one of the methods described above.