Radiant Heating Workbook

Radiant Heating Workbook

Insulating a Radiant Slab

How much insulation is necessary under a typical radiant slab?

2 MIN READ
Siegenthaler says 2-in. under the slab

Siegenthaler says 2-in. under the slab

This article is part of the Radiant Heating Skills Workbook.

Q. How much insulation is necessary under a typical radiant slab?

A. John Siegenthaler, a consulting engineer who specializes in hydronic-heating-system design, responds: Downward heat loss from a radiant slab should not exceed 10 percent of upward heat output, a ratio derived from European installation standards for floor heating systems. It’s possible to calculate the R-value needed to meet this goal while accounting for such factors as floor coverings, soil temperature, and required upward heat flux. But lately, I’ve begun simply specifying a minimum of 2-inch extruded polystyrene insulation under all heated slabs, even those in basements with no floor coverings. Here’s why:

In my area, the cost difference between 1-inch-thick and 2-inch-thick extruded polystyrene insulation board is currently about 48 cents per square foot. Using 2-inch rather than 1-inch extruded polystyrene adds about $720 [2009 prices] to the cost of insulating under a 1,500-square-foot slab.

To maintain a seasonal average slab temperature that is 10°F above the seasonal average soil temperature through a heating season lasting from October 1 through April 30, a slab insulated with 1 inch of foam would lose 7.1 million Btu more than a slab insulated with 2 inches of foam. Although the rates of downward heat loss from the slab differ by only about 0.93 Btu per hour per square foot, this difference translates into a lot of money over the course of the entire heating season.

Assuming heat was supplied from fuel oil purchased at $3.75 per gallon (a high price for 2009; for current average fuel oil prices, see the EIA ) and burned in a boiler with an AFUE of 85 percent (a very low AFUE), the savings associated with the thicker insulation would be $224 per year. That makes the simple payback on the 2-inch underslab insulation about 3.2 years, which far surpasses the economic returns associated with solar energy systems, wind turbines, and quite a few other more “newsworthy” energy alternatives. For more efficient boilers and either less expensive oil markets, or markets with a range of less expensive fuel options, the payback is even faster.

Be sure to check out the rest of the Radiant Heating Skills Workbook.

About the Author

John Siegenthaler, P.E.

John Siegenthaler, P.E., operates Appropriate Designs, a building systems engineering firm in Holland Patent, N.Y. He is the author of the course materials for the ASSE 19210, Hydronics Heating and Cooling Installer Professional Qualification Standard, as well as the author of "Modern Hydronic Heating for Residential and Light Commercial Buildings," and “Heating With Renewable Energy” (both published by Cengage).