Cooling vs.
Dehumidification
The graph in Figure 1 of the article "Air Conditioning for
Humid Climates" (10/04) is misleading. The caption of the
original figure, from a 1999 publication, indicated that it
represented the annual sensible and latent loads for cooling
ventilation air — that is, the annual load to cool one
scfm of 100 percent outside air down to space conditions. The
article implies that these are annual room cooling loads for
one scfm of air. But 95 percent of residential systems process
only return air, not 100 percent outdoor air. The outside air
load comes from return duct leakage if the return leak is in
the attic or crawlspace, or from infiltration. The statement
that "on a hot, humid day in a house with a properly sized
5-ton cooling system, 3 tons of that capacity might be working
to dehumidify the air, while 2 tons are working to actually
cool it" is just plain wrong.
Donald P. Gatley, P.E.
Atlanta
Sheathing Not
Water-Repellent
In December's Q&A, editor Don Jackson stated that the
IRC (2003) does not require a vapor barrier behind brick veneer
when a 1-inch air space is provided between the plywood or OSB
sheathing and the brick. I'm afraid Mr. Jackson got it only
partially correct. The IRC does allow the vapor barrier to be
deleted, given the 1-inch air space, in accordance with Table
R703.4, but only when a "water-repellent sheathing" is used
(footnote m). There are a number of sheathing materials I would
consider water-repellent, but plywood and OSB are not among
them. These materials are more water absorbent than repellent
unless they have been treated with a water-repellent
coating.
As a general rule, we require a vapor barrier over plywood or
OSB sheathing when brick veneer is being installed. If a
builder could provide sufficient information to convince me the
plywood or OSB sheathing he was using was water-repellent, I
would have to allow it. To date, that hasn't been an issue,
because the builders recognize the importance of the vapor
barrier in keeping moisture out of the wall assemblies.
Thanks for your excellent publication.
Arthur E. Berkley, CBO
Director of Inspections
Isle of Wight, Va.
Editor Don Jackson responds: Thanks for
your comments. Your letter points up how confusing these issues
and the code itself can be. First, to clarify, "vapor barrier"
— or "vapor retarder," as the IRC calls it (R318)
— usually refers to the warm-side membrane (typically
6-mil poly) installed to keep water vapor out of wall and
ceiling cavities. The code uses the term "weather-resistant
sheathing paper" (R703.2) to refer to housewrap and felt paper
installed over exterior sheathing.
What I said in my original response was that while the IRC
doesn't require the building paper in the case you mention
above, both the Brick Industry Association and the APA
recommend it and it shouldn't be left out.
As for the code definition of "water-repellent," check R604.3,
which reads: "Wood structural panels marked Exposure 1 or
Exterior are considered water-repellent sheathing under the
code." But I wouldn't change your policy based on this.
It's a somewhat moot discussion, anyway, because rarely do you
see a full 1-inch cavity in residential brick veneer work. Even
if you did, leaving off the building paper would still be a bad
idea, as most everyone — except perhaps the IRC
— agrees.
Smaller Is Greener
According to "Strictly Green in Vermont" (In the News, 12/04),
Vermont Builds Greener is the only green-building program with
a house-size factor. That is not true: The Earth Craft Program,
which is used in Atlanta and is about to be adopted by the Blue
Ridge Home Builders Association in Charlottesville, Va., has a
three-step point award. Houses between 2,200 and 2,500 square
feet get two points; houses between 1,800 and 2,100 square feet
get four points; and houses under 1,800 square feet get six
points.
Linda Lloyd
The Quarries ecoVillage
Schuyler, Va.
Manufactured Stone
The article on manufactured-stone veneer (12/04) highlights a
key issue for the building industry. Regardless of the
material, no cladding system is durable if improperly
installed. In every instance where the author found a problem,
the culprit was not the cladding but missing or inadequate
flashing, improper treatments around windows and doors,
incorrect transitions from one material to another, or damaged
or incorrectly installed weather-resistant barriers.
With four decades of experience in the manufactured-stone
veneer industry, we know that the author's point is correct:
Without exception, adherence to building codes and good
building practices prevents moisture problems.
Manufactured-stone veneer, when properly installed, can be a
high-performance cladding that adds beauty and durability to
any structure.
Herbert Slone, R.A.
Technical Services
Owens Corning
Twin Lakes, Ohio
Sub-Slab Moisture Membrane
In November 2004 Products, you outlined a way to stop seepage
by using Delta-MS air-gap membrane under the slab. The featured
technique, which requires a "waste" slab, is used only in
unusually severe moisture conditions.
The standard method is simpler and costs less; no waste slab
is needed. The Delta-MS can be laid directly on the gravel
substrate, with seams overlapped by 6 inches and taped with
vapor tape. When the regular floor slab is poured on top, the
seams are also sealed by compression. Combined with Delta-MS on
the perimeter walls, this technique provides good moisture
protection.
The cost of the membrane is around 40 cents per square
foot.
Tom Fallon, Vice President
Cosella Drken Products
Beamsville, Ontario
Efficient Fireplaces
I enjoyed Katie Hutchison's observations about fireplaces
(Design, 1/05). I take issue, however, with the statement that
a Rumford design is efficient. While it will radiate more heat
back to the occupants than a standard firebox design, it's far
from efficient. The same is true of a standard fireplace. Both
fireplace types lose huge amounts of the warmest air in the
building to the draft. If the damper is left open after the
fire is out, the heat loss may well exceed the heat gain from
the fire.
A better solution would be a zero-clearance fireplace with
glass doors and an outside air kit. Better still is a wood
stove or fireplace insert. Probably the most efficient is a
masonry heater, of the type used in Northern Europe,
Scandinavia, and Russia. They use small-diameter wood burned at
extremely high temperatures. This ensures complete combustion,
with very little uncombusted material. The heat is stored in a
massive masonry structure, which emits it slowly into the
building. These aren't cheap, and should be designed by someone
with experience in their design, but they can approach 70
percent efficiency.
Bruce Donelson
O'Brien, Ore.