by Russell J. Kenney & Michael E.
Kenney
The exterior insulated finish system, or EIFS, has been on
the market in America since the early 1970s. EIFS came here
from Europe, where it had been used successfully since the late
1940s, gaining popularity as an effective and affordable way to
renovate older buildings and restore buildings that were
damaged in the Second World War.
Unfortunately, the version of EIFS that was brought to this
country was very different from the system that had worked so
well in Europe. Modifications were made to the system with very
little testing and engineering analysis. Problems started to
crop up soon after EIFS entered the U.S. market, and as most
people know, North America had widespread EIFS failures in the
1980s and 90s. Our company has prospered investigating many of
those problem installations, serving as consultants in court
cases involving everything from houses to high-rises.
We've learned a lot about why and how EIFS can fail, but we
haven't given up on it as a system. EIFS has advantages: It's
fast, it's economical, and it offers a lot of control over
style and appearance. And done right, it works. If you
understand the design issues, the materials, and the
installation process, you can get good results with EIFS. We
don't just investigate failures — our company has
supervised millions of square feet of EIFS work on new and
existing buildings, and we have confidence that those
installations will perform acceptably.
As a result of our investigations of EIFS problems on
buildings nationwide, we've proposed a number of changes in
American codes and standards that apply to EIFS. Some of our
recommendations have been adopted by the codes or by
manufacturers, and some haven't. Since everyone hasn't seen fit
to change their specifications, we've developed our own
standards for jobs we supervise.
Our company reviews plans, writes specifications, and
inspects or supervises EIFS work on site. We provide advice on
system design, materials selection, and installation methods.
How the system is installed is usually the critical factor, but
the design and the materials can also affect performance.
Barrier EIFS Versus Drainage
EIFS
To put EIFS cladding on a building, the EIFS contractor first
attaches expanded polystyrene (EPS) insulation board to the
wall structure. This rigid foam base then gets covered with a
base coat formulated from water, acrylic polymer, Portland
cement, aggregates, and fillers. Fiberglass reinforcing mesh is
embedded in the wet base coat. After the reinforced base coat
sets up, all joints are sealed with caulk or sealant; a finish
coat is applied to the whole system for color and texture. The
result is a (mostly) waterproof skin with an attractive
appearance.
In the original EIFS system, the insulation board was
attached directly to the building with adhesive, and the base
and finish coatings (along with the sealants) were the
building's main defense against rain. That system is called
"barrier EIFS," and it has worked well on concrete and masonry
buildings in both Europe and America. Over time, there are sure
to be cracks in the lamina (composed of base coat, mesh, and
finish coat), as well as partial sealant failures at joints;
but concrete and masonry buildings don't tend to suffer damage
from the relatively small amounts of water that pass the
exterior weather barrier.
Buildings made with water-sensitive materials are a
different story. If a building has wood framing and OSB
sheathing (or light-gauge steel framing and gypsum board
sheathing), the amounts of water that enter the wall through
window assemblies, at interfaces between EIFS and abutting wall
components, or through cracks in the EIFS lamina are sufficient
to do serious damage to the structure below. The EIFS may look
great on the exterior, but underneath, the building could be
disintegrating. As the substrate deteriorates and the bond
between the building and the EPS weakens, the foam and lamina
experience more movement, the cracking gets worse, more water
enters, and the problem grows. Sometimes large areas of EIFS
can lose their bond to the building and hang loose, held in
place by nothing but the caulking around the windows. In the
end, the wind may tear off whole sections of the exterior
cladding. For wood buildings, hidden structural rot can be
fatal.
We've investigated commercial buildings where underneath the
EIFS, some of the backup walls were constructed of concrete or
masonry, and other sections were made of steel framing with
gypsum board sheathing. Often in those structures, the masonry
sections are in good shape, with the EPS still well attached,
while the parts of the building with a moisture-sensitive
backup wall are basically falling apart. The difference comes
down to how well the substrate can tolerate moisture.
That doesn't mean that EIFS is restricted to masonry
buildings. It can be effectively installed on a wood-sheathed
or gypsum-sheathed structure. But wherever the sheathing
consists of moisture-sensitive substrates like OSB or gypsum
board, we recommend a "drainage EIFS" (also called
"water-managed EIFS") design. This is also what the newer
versions of the model codes require for residential
construction (although not all jurisdictions have adopted that
change). Since almost all houses are wood-framed with
moisture-sensitive OSB or plywood sheathing, residential EIFS
in general should be a drainage system.
Drainage EIFS Details
In a drainage EIFS system for wood-frame buildings, the wall
is first covered with a protective water-shedding drainage
plane material; then mechanical fasteners are used to attach
the EPS board to the wall system (see Figure 1). This works
well in buildings sheathed with plywood or OSB. (For commercial
buildings that use gypsum sheathing, there are also drainage
EIFS systems that rely on a liquid or troweled-on waterproofing
layer and use adhesively attached EPS, but these are seldom if
ever used for residential work.)
Figure
1. A drainage EIFS system relies on a drainage
medium such as asphalt felt paper or housewrap to
protect moisture-sensitive parts of the building
against water that gets past the surface coatings. Foam
board is attached over the drainage plane using
mechanical fasteners; then base coat is troweled onto
the foam, and fiberglass mesh is embedded in the base
coat. Finally, a finish coat is applied over the
reinforced base coat. Effective flashing details and
joint sealing are critical to the success of the
system. |
Major EIFS manufacturers that supply drainage EIFS systems
all have some sort of requirement for creating an air space or
capillary break between the EPS board and the drainage material
covering the wall. One method is to use a "crinkle wrap"
variety of housewrap such as Tyvek's StuccoWrap. Another method
is to use a type of EPS board that has a grooved, wavy, or
waffled back profile, so that the board contacts the wall only
in spots, creating drainage channels between the board and the
weather-barrier drainage material. Both systems work
acceptably.
In fact, we've tested EIFS systems using ordinary
flat-backed EPS board over regular housewrap or asphalt felt
and found that drainage occurs readily even without the
"drainage channels." If you apply the EPS board flat to the
paper, apply base and finish coats in the regular way, then cut
a hole in the EIFS eight or ten feet up the wall and actually
pour water in, you'll soon see the water drain out through the
weep holes in the drainage track at the bottom of the wall.
Water drains behind the EPS, as well as through it. It's true
that our own specs, like the major manufacturers' specs, do
call for drainage-channel EPS board or crinkled housewrap, but
that is mainly because we want the warranty to hold.
The "secondary weather barrier" beneath the EIFS should
include not just a water-shedding drainage material (typically
asphalt felt or housewrap), but also a system of flashings for
all penetrations in the envelope, including windows, doors,
outside lights, dryer vents, hose bibbs, and exterior electric
outlets. Transitions where exterior decks are attached or where
roofs abut walls also need foolproof flashings. All the
flashings have to be integrated with the water-shedding
drainage plane so that water flowing downward will always go on
top of the drainage material, not behind it. Before the EIFS
goes on, you should be able to spray the whole building with a
hose and have no water contact the framing or sheathing.
To work right, the whole drainage plane system has to be
carefully considered and properly installed. We've created some
standard flashing details that are adaptable to most
situations, but it's not possible to design a standard detail
that will cover every possible scenario. In unusual cases, the
trick is to "think like a raindrop." Water on a surface will
generally seek to go down, although it may travel sideways or
even up when it contacts very small cracks and capillary
openings. When you come to a building element that calls for a
custom flashing detail, just make sure that gravity will pull
the water down and away from the wall, without bringing it into
contact with fine cracks or narrow openings.
EIFS Materials and
Installation
When the secondary weather barrier is done right, the building
will be resistant to water damage even if the EIFS, windows, or
caulking has some leaks. Nevertheless, the EIFS also should be
installed correctly. The more waterproof and durable the EIFS
skin, the better. Installation details matter, and so does the
choice of materials. The goals are to prevent leaks, to resist
weathering, and to minimize cracking and sealant failures over
time.
Our company has investigated every material used with the
EIFS system — the EPS board, the base coats, the
fiberglass mesh, the sealants, and the finish coats. We've
noticed that the European standards for most of those materials
are stricter than the American standards, and in most cases, we
believe that the stricter European standards are better.
Unfortunately, because of the relatively weak U.S. industry
standards, it's not always possible to get the same materials
in America that are available in Europe. EIFS made with
American materials may be less durable than EIFS in Europe,
even if the installation details are the same (all the more
reason to be careful about the secondary weather barrier).
However, given what's available on the U.S. market, it's still
worth the effort of choosing materials carefully and applying
them correctly.
In our jobs, we use materials supplied by the major
manufacturers that have been in the EIFS business for many
years: Dryvit, Parex, Senergy, and Sto. However, all those
companies offer installers a menu of choices in drainage wrap,
EPS board, reinforcing mesh, and coatings. Our specs call for
certain choices from that menu.
. EIFS requires a
soft insulation board that can move without cracking (Figure
2). Because it must be soft, the board is not dense, and the
nominal one-pound EPS board that is typically used for EIFS is
not watertight. In Europe, EPS board is generally made using a
vacuum process that results in a denser, less porous board.
American EPS is most often made with a steam process and is
generally less dense and more porous. The American
manufacturing standards for a nominal one-pound-density board
require an actual density of only .9 pounds per cubic foot; but
in tests we have performed, most boards on the market achieve
that density barely, if at all. The standards also allow the
board to absorb 2.5 times its own weight in water; in effect,
the foam is allowed to be a sponge.
Figure 2.A worker attaches soft EPS
"beadboard" with screws to form the base of the EIFS
cladding. The close-up, below, shows the voids between
the plastic beads. EPS allows water to leak through and
can hold moisture against the building. That is why
careful joint sealing and an effective secondary
weather barrier are critical to system
performance. |
Water can take minutes or hours to pass through EPS board,
depending on the density of the board. But in any case, the EPS
generally does not protect the house against water. Water that
gets to the foam will trickle through it or through joints
between foam pieces, and if the water can't drain out, it will
collect at low spots. Trapped moisture in the foam can create
moist conditions next to the wall. So it's critical to prevent
cracking in the EIFS surface, to seal all joints effectively,
to detail the secondary weather barrier carefully, and to allow
drainage throughout the system.
For mechanically attached EPS, our spec calls for foam boards
greater than one inch thick.