JLC Field Guide: Insulating Foundations

Below-grade heat loss can be significant in colder climates. And as with any structure in the ground, you also have to pay close attention to water and moisture issues. But the marriage of moisture and insulation is not always a happy one.

2 MIN READ
Insulated Foundation Systems

Insulating Foundation Walls

Foundation walls give up a significant amount of heat. Insulate poured-concrete and block foundation walls with a minimum of 1 in. of extruded polystyrene insulation. Expanded polystyrene (EPS), polyisocyanurate, and polyurethane rigid insulations are not recommended for below-grade applications.

Cold-Climate Foundation Insulation

Install insulation running the full height of the foundation wall. In cold climates, “taper” exterior foundation insulation as follows:

  • Install 1-in.-thick 2×8-ft. tongue-and-groove sheets vertically from footing to sill plate.
  • Next, place a second layer of half-sheets (2×4-ft.) extending down 4 ft. with joints offset.
  • Follow with a third layer of 2×8 sheets running horizontally across the top of the foundation.

Insulation Protection

Protect vertical insulation on the exterior of foundation walls with 3/8- or 1/2-in. pressure-treated plywood or a parging coat of Type M or S mortar applied over expanded-wire metal lath (see Stucco).

Insulation for Unheated Garage Slabs

An unheated structure, such as a detached garage, needs continuous insulation under the entire slab, extending out beyond the perimeter (below). Since there is no building heat to capture, this insulation is intended to prevent earth heat from escaping.


Foam for Frost-Protected Shallow Foundations

In this design, the footing and slab are bearing on the foam. By code, the foam used for frost-protected slabs must have a density of 2 lbs. per cu. ft. Most expanded foam stocked by lumberyards is only 3/4-lb. or 1-lb. density and lacks sufficient compressive strength. High-compression foam usually needs to be special-ordered.

Insulation for Walkout Basements

The principle of frost protection can also be applied to special cases where foundation elements are vulnerable to frost, such as walkout basements (below). In these cases, carefully placed insulation can prevent frost action from damaging or moving structural elements.

Insulation for Piers

In some soils, even a 48-in.-deep post footing will sometimes be heaved up by frost. Post-and-pier foundations for decks and porches can be frost-proofed, using a 4-ft. strip of foam around post footings to keep the ground below from freezing (below).