EIFS — exterior insulating finish system — has
been a popular alternative to traditional stucco and brick
— that is until its failure rate started to increase (see
"EIFS Under Scrutiny," Eight-Penny News, 4/96). EIFS is a
"barrier" system that relies on coatings and sealants to make
every square inch of the house shed water 100% of the time. But
because building materials expand and contract and caulking
doesn’t last forever, even a perfect barrier-EIFS
installation is bound to let some water in. And since an EIFS
home is covered in insulating plastic foam, whatever water goes
in stays in.
It doesn’t take a big leak to do big damage —
once a wall is affected, framing, windows, doors, sheathing,
insulation, even interior drywall and finish flooring may have
to be removed and replaced.
Water-Managed Systems
An
alternative to barrier EIFS is a water-managed system. In a
water-managed system, it’s assumed that the installation
will not be perfect and that some water will eventually
penetrate the building’s skin. A managed system directs
that water back to daylight, and allows the wall system to dry
out before damage can occur. Some EIFS manufacturers —
Senergy and Sto, for example — now offer a managed
drainable EIFS, which has great potential. In North Carolina,
however, where failures have been rampant, builders and
homeowners are still dubious about all foam systems. For my
EIFS replacement work, I need a non-EIFS alternative, and
USG’s Duro-Screen 1000 system fits the bill (see Figure
1).
Figure
1. USG’s water-managed system uses Durock cement
board over a moisture-resistant drainage plane. Any water
leaking past the stucco skin is directed to weep holes at the
bottom of the wall.
Instead of rigid foam board, DuroScreen uses Durock cement
board and other components to create a drainage plane between
the sheathing and the stucco skin, allowing any water that
penetrates to escape.
Assessing the Damage
After
fixing more than 40 of these EIFS-clad homes in the Greensboro,
N.C., area, I’ve concluded that all EIFS replacement
projects have one thing in common: The total damage can’t
be determined until the house is stripped of the EIFS, so there
is no way to price the job ahead of time. The most vulnerable
places are always around windows and doors, and where first
floor roofs meet second floor sidewalls. After a visual
inspection, we can use a hand-held moisture meter with long
probes to determine how much of a given wall is involved.
We’ll do three "snake bites," penetrating the foam first
directly below the problem area, and then down the wall in
1-foot increments. Moisture content above 19% in the underlying
structure spells trouble.
I charge by the hour to do the initial investigation, then
provide a fixed price per square foot to remove and replace the
EIFS with a water-managed system. All repairs to the structure
are handled separately on a case-by-case basis, and the scope
of work and cost can vary wildly, depending on the extent of
the damage.
Preconstruction Meeting
A
week or so before the work starts, I schedule a meeting with
the homeowner, architect or building designer, the engineer if
there is one involved, a USG field representative, and any
other subcontractors who will be involved on the job. My main
goal is to acquaint everyone with the proper details of the
system, particularly the flashing details that will be
necessary for the finished product, such as the
roof-to-sidewall "kick-out" flashings. Much of the water damage
I’ve seen on EIFS as well as traditional stucco could
have been avoided if the various parties had met first to
coordinate the details.
Next, I inspect the house to locate as many water damaged
areas as possible. In areas around windows, it’s
important to get underneath the cladding to assess the
carpentry work that will be needed. At this point, I get the
subtrades involved, because their repairs could hold up the
rest of the process.
Case In Point
One of the
tear-off and replacement jobs I recently completed was on a
7,000-square-foot home in an upscale subdivision of Greensboro,
N.C. The $1.7 million home was only three years old when the
owners discovered extensive water damage behind the barrier
EIFS exterior (Figure 2).
Figure
2. This three-year-old Greensboro, N.C., home was
damaged when water leaks around windows and poorly-flashed
roof-wall connections became trapped behind the EIFS cladding
(left). Even window trim, jambs, and sills were rotted (rifht)
and had to be replaced.
Whole sections of the OSB sheathing were blackened and
rotting. Both the sheathing and the fiberglass insulation in
the wall cavities were still wet and moldy. Most of the
home’s 40-plus windows had rotting sills and mullions
— in fact, mushrooms were growing out of some of the
sills. We discovered a colony of carpenter ants in the
structure, and shelf fungi were growing inside the wall
cavities. The home required the replacement of all windows, all
the OSB sheathing and insulation, some door frames, much
flashing, and many of the studs, as well as the entire barrier
EIFS stucco system.