Lessons From Florida's Hurricanes: Why Stucco Walls Got Wet
- Continued
On the other hand, our testing of windows and window assemblies
indicates that many of them leaked under conditions well below
their listed, rated value. In fact, many tested windows leak
under a simple water spray with no wind pressure at all.
Factory testing of windows seems to be missing a widespread
incidence of leakage at the window-assembly corners. Also,
windows are tested as single units, but are often sold as
preassembled "mulled" units, with two or more windows combined
in a composite arrangement. Every preassembled mulled unit we
tested leaked at zero wind pressure (Figure 7).
Figure 7.Factory-assembled windows like this
double unit (top left) are frequently found to leak at the
corners (top right) and the center joint (bottom).
From our visual inspections of windows in the field, and from a
closer look at some randomly selected windows that we took
apart, it seems clear that there is a widespread problem with
the connections between the windowsill and the window jamb:
Windows delivered to the site are likely to be leak-prone
before installation.
Window installation is also an ongoing concern. The methods
used in Florida, as elsewhere, often don't ensure reliable
water management. In particular, precast concrete windowsill
components sold into the Florida market are shaped in a way
that directs some leakage into — rather than out of
— the building (Figure 8).
Figure 8.Precast concrete
windowsills for block walls (top two photos) have a profiled
flange attachment rib that directs some leakage toward the
interior (middle). A better windowsill design would direct
water toward the outside (bottom).
It would be good if windows delivered to the job could be made
to hold water out more effectively. But in the meantime,
builders have to be aware of the limited water resistance of
window units, and design walls that are tolerant of window
leakage.
Paints and Coatings
When we first went to Florida, some people had the idea that
we would focus on paints and coatings. Many observers had
noticed that homes only a year or two old had shown more
leakage than homes that had been around for five or 10 years,
and they thought perhaps this was because successive
repaintings had sealed all the microcracks in the stucco. If we
required a high-build elastomeric paint on new homes in the
first place, the reasoning went, maybe we could prevent the
whole problem.
That idea makes sense, but it doesn't hold up completely. For
one thing, all those older buildings were repainted (and the
cracks patched using other means as well) only after they had
been through the process of shifting and had settled down to
some kind of equilibrium. There are very few paints and
coatings around that can span the shrinkage cracks in a new
building and also stay intact as the building shifts and cracks
over its first few years. So while patching and painting a
stucco wall is a good idea — in fact, it's necessary
maintenance — and it has to be done continuously over the
life of a building, it is particularly important during the
first two or three years.
Also, high-build paints and elastomeric coatings span
microcracks most effectively when the surface is smooth. On
rough-surfaced stucco, which is a very common finish in the
industry, coatings are much less effective at sealing surfaces
(Figure 9).
Figure 9.Paints and coatings are not highly
effective at spanning cracks and pinholes in a rough stucco
coating. Ordinary paint (top left), a 3-mil high-build coating
(top right), and a 10-mil elastomeric coating (bottom left) all
leave pinholes that can be seen under magnification. Thick
elastomeric coatings over stucco can also be prone to
blistering (bottom right).
And to gain flexibility and crack-spanning ability in a
coating, you often have to give up vapor permeability, so that
the coating may tend to trap moisture within the stucco as well
as keep bulk water out. That trapped moisture can cause
coatings to blister. Modified stucco mixes may even re-emulsify
and turn to goo when you trap moisture in them with a
low-permeability coating.
That said, specialty elastomeric coatings hold great promise.
The "holy grail" of coatings research has always been to
develop a highly elastic coating that also breathes. We're not
sure how much it needs to breathe, but generally I think the
perm rating should be 10 or higher. And, for the present,
specialty coatings should be applied to stucco only by
knowledgeable installers. "High build" acrylic paints that get
you 5 to 6 mils of thickness at permeabilities of greater than
10 perms are pretty much the optimum performance limit with
conventional coating systems.
Improving Masonry Mass Walls
Clearly, masonry-block walls — as commonly built in
Florida and other places — have a limited capacity to
hold and drain water. When cracks and crevices in the wall
assembly are full, water trickles onto interior floors at the
base of walls. Saturation of walls also leads to humid
conditions on interior wall faces, sometimes allowing mold or
mildew to grow.
Two proven methods would improve the performance of these
walls. First, the foundation slab or footing should be built
with a stepped-down seat or shelf where the first course of
masonry block is set, as in Figure 10 (previous page). This
will direct water that reaches the base of the wall outward to
the outdoors, rather than inward, where it can damage floors or
cause humidity problems.
Figure 10.To help block walls store greater amounts
of incidental water and to direct the moisture back outside
rather than allowing it to trickle into the home, foundations
should have a stepped-down shelf at the slab edge. A weep
screed at the lower termination of the stucco will allow
accumulated water to get out.
The interior-wall face will perform better if covered with a
continuous layer of semipermeable rigid insulation, such as
commonly available extruded polystyrene (Figure 11). This will
reduce vapor migration into the home as well as condensation,
preventing moisture from accumulating in the home's
drywall.
Figure 11.Extruded polystyrene
insulation applied to the inside face of the block wall, to the
outboard of the interior furring, or to the wall framing will
allow some drying by vapor diffusion to the interior, but will
direct bulk water downward toward the base of the wall, where
it can escape to the outside.
Refining Drained Frame Walls
Wood-frame stucco-clad walls should have a bond break layer
installed between the stucco rendering and the drainage
plane.
In practice, this means applying two layers of building paper,
or one layer of building paper over a layer of plastic
housewrap, before applying stucco. At the joint between drained
upper-story assemblies and mass-wall lower-story assemblies, a
weep-screed flashing should be installed, as in Figure
12.
Figure 12.So that horizontal control joints between
floors direct water to the outside of the wall, first apply a
bridge flashing between the wood frame wall and the block wall
below, and then attach a weep-screed flashing that overlaps the
lower wall (top left). The primary drainage-plane membrane
should then be installed overlapping the weep screed (top
right) before a bond-break paper layer and wire lath (bottom
left) are put in place. Finally, stucco can be applied to both
walls (bottom right).
Window and Flashing
Recommendations
There is a problem in Florida and other states where high-wind
codes are taking effect that is caused by the contradictions
that arise between two imperatives: the obligation to ensure
structural integrity and the need to keep out water. In many
cases, building officials are enforcing fastening schedules and
structural connections at the expense of proper flashing and
drainage details.
To fix this problem, all of us — including builders,
code officials, and manufacturers — need to think through
what we're doing when we attach a window or other component to
a wall assembly. Here are a few things to consider:
First of all, whether it's a window, a dryer vent, or a hose
bibb, when you install something through a wall, you have to
flash the opening. Second, drainage assemblies for windows have
to extend all the way to the back of the window, because
windows can leak at any point. And, finally, flashings above
windows and other penetrations have to catch water from all the
way to the back of the cladding system, and have to direct it
all the way to the exterior of the building.
Maintenance and Crack Repair
Stucco cracks have to be addressed with ongoing homeowner
maintenance. The best practice is to allow stucco walls a
reasonable "breaking-in" period, from one to two years. By
then, most if not all of the cracks that are going to appear
will already be evident. At that point, cracks should be
individually sealed with caulking or a brush-in cementitious
crack-repair formula, and then the walls can be
repainted.
Inspecting walls every few years, and repairing them in this
fashion as needed, should be enough to keep a stucco wall
performing well for many decades.
Joe Lstiburek, P.Eng.,is a principal of Building Science Corp.
in Westford, Mass., and an investigator of moisture-related
building problems.