A.Paul Eldrenkamp, owner of
Byggmeister, a custom remodeling firm in Newton,
Mass., responds: Eaves areas behind knee walls
are notoriously leaky. If you run hvac ducts in
that space, you complicate things even more
— especially if the ducts are also
leaky.
It would indeed be a good idea to bring that
eaves area — and particularly those ducts
— into the conditioned part of the house.
This means that the insulation and the air barrier
need to be in the rafter plane rather than in the
knee wall. Stuffing fiberglass batts in the rafters
will provide the insulation but not the continuous
air barrier. You'll probably have to use housewrap
or rigid foam in conjunction with the fiberglass,
or use spray foam for a less labor-intensive
job.
I would not use polyethylene as an air barrier
in that area (current best practice for any but the
coldest climates seems to be to avoid polyethylene,
to allow for drying). And don't forget that the
rim-joist area needs to be insulated and air-sealed
as well. The insulation/air barrier should be
continuous: roof plane sealed to rim joist, rim
joist sealed to wall plane, with no gaps in
between.
Regardless of what materials you use, you're
going to have a hard time knowing if you got the
job done right without doing a blower-door test.
You should be able to run the blower door and not
find any significant air leakage out of the
knee-wall access hatches — or out of any
penetrations between the eaves area and the living
quarters, for that matter. Air leakage would
indicate that there's too much communication
between the eaves area and the outdoors.
Your local utility should be able to help you
find a diagnostician with a blower door. The Web
site of the Energy Conservatory
(www.energyconservatory.com), supplier of the most
readily available blower-door equipment, also has a
list of airtightness testing contractors, organized
by state.
You should also try to determine the source of
the moisture that's condensing on the framing. It's
worth checking the relative humidity at various
places in the house. Test the basement, too:
Air-transported moisture from a basement or
crawlspace could easily travel up a duct chase to
an eaves area and condense on a cold surface. (The
blower door can help identify such leakage paths.)
Anything with more than 50 percent relative
humidity in the winter is possibly worth some
remedial action.
It may be that the insulation and air-sealing
strategies described above will solve the problem
just by warming the eaves area up above the dew
point, but it's always worth considering a
two-pronged approach: One, stop the leakage of
humid air into cold cavities; and two, control the
humidity of the air to begin with. If you're
getting only a small amount of condensation, and
only on the coldest days, your challenge is
probably primarily air-sealing rather than humidity
reduction.
By the way, if someone's at the house doing a
blower test, it's worth paying extra for a
duct-leakage test, too.