I’ve installed and repaired a lot of siding in the Des
Moines, Iowa, area over the last 30 years — enough that I
now specialize in troubleshooting and consulting on exterior
renovations. When a builder or homeowner calls me about a water
intrusion problem, I usually find that shoddy workmanship or
poor detailing led to a materials failure. However, in the case
of the nine-month-old house shown on these pages, the source of
the problem was less obvious.
The original builder had responded to homeowner complaints
about dampness and water stains around a window — a
double unit centered in a facade clad with manufactured-stone
veneer — by reflashing it. But his repair only seemed to
make the problem worse, so he asked me to help find the source
of the leakage and suggest a way to fix it. When I inspected
the house, the room where the window was located smelled musty,
there were obvious rust and water stains on the window itself,
and the carpet was wet. The moisture content in the drywall at
the bottom of the wall was 70 percent, according to my moisture
meter.
On the exterior, the manufactured-stone cladding looked
undamaged, but I strongly suspected that the problem
wasn’t just a leaky window. Because new flashing
hadn’t helped and there weren’t any other obvious
explanations for the leaks, my recommendation was to remove the
stone cladding and start all over again.
After most of the stone veneer and mortar base coat had been
removed and the OSB sheathing exposed, moisture readings
confirmed my suspicions: Water was getting behind the cladding
and migrating into the wall system — not just around the
double window, but everywhere (see Figure
1).
Figure 1. Though it looked sound from the outside, the
manufactured- stone veneer on this nine-month-old house was
absorbing water and soaking the mortar base coat (left) and the
sheathing and framing underneath. The only way to fix the
problem was to pull off the stone (right) and install a proper
substrate.
Although the problem was clearly worst around the window, there
were elevated moisture levels at the corners of the facade and
above the window, as well as in the stone veneer remaining on
the wall. Below the window and at the base of the wall,
moisture content readings in the wall sheathing exceeded 90
percent.
To look inside the wall cavity, we removed the window and
opened up the wall from the outside in several places. We found
that the bottom plate was saturated, with a lot of condensation
on the plastic vapor barrier. Insulation pulled from the cavity
under the window was wet on both its top and bottom edges, and
water was clearly wicking up the studs. The smell of mildew was
potent.
Installation Details
Like brick, manufactured-stone veneer is a reservoir cladding,
meaning that it absorbs and holds water. But it isn’t
installed over an air space, as brick is. Instead, the
lightweight cement-based product is installed in a mortar
setting bed applied over a stucco-like mortar base coat. There
is no drainage space to allow saturated material to dry
out.
With traditional stucco, the base coat is applied over a double
layer of asphalt-saturated building paper. As the paper absorbs
moisture in the mortar, it swells. When the mortar cures and
the assembly dries, the paper shrinks and wrinkles, creating
drainage pathways behind the stucco. To allow water to drain
out of this type of assembly, weeps are installed wherever
there is a bottom termination, such as above a window or at the
base of a wall.
Because manufactured-stone veneer can hold even more moisture
than stucco, similar measures should be used underneath it,
particularly in wet climates. Unfortunately, there really
aren’t any uniform industry guidelines or building code
requirements for its installation. While stone manufacturers
specify some sort of weather-resistive barrier (WRB), they are
often vague about the details and defer to local building-code
requirements; most don’t even mention the need for
weeps.
In fact, the builder of this house followed the veneer
manufacturer’s installation instructions, installing a
layer of Tyvek housewrap beneath a layer of 15-pound felt
paper, a WRB clearly inadequate for the climate in our part of
Iowa. Without any way for water to drain out, the wall was
bound to leak sooner or later.
The Fix
For this project, we adopted details developed by Owens-Corning
for its manufactured-stone veneer, a product called Cultured
Stone (see “Best Practices for Flashing Details” at
culturedstone.com click on Technical Info).
But we upgraded the WRB to include a layer of DuPont Tyvek
StuccoWrap (800/448-9835, www2.dupont.com) covered by two layers of
Fortifiber Super Jumbo Tex 60-minute building paper
(800/773-4777, fortifiber.com), a vapor-permeable
asphalt-saturated kraft paper (see
illustration).
Substrate and Flashing
Details
A double layer of building paper installed over StuccoWrap
creates a drainage plane beneath the mortar base coat.
Galvanized metal weep screeds at the top of the window and at
the base of the wall allow water to drain out of the
assembly.
Since most of the leakage occurred around the window opening,
we were careful to detail the WRB and flashing properly when we
reinstalled the window in the wall (Figure 2).
We used DuPont FlexWrap, a flexible flashing tape, to create a
sill pan at the bottom of the opening. Then we reset the window
in a bed of sealant at the nailing flange, finished wrapping
the wall with StuccoWrap, and sealed the window nailing flanges
to the wrap with StraightFlash self-adhering flashing
tape.
Figure 2. A sill pan fashioned from FlexWrap (far
left), installed on top of the StuccoWrap, protects the rough
window opening. The window is reinstalled with the nailing
flanges set in sealant, then taped to the StuccoWrap
(left).
We also used flashing tape to seal the top of the window to the
sheathing, and to seal the joint where the veneer intersects
with the home’s horizontal vinyl siding — a tricky
area to detail properly, and one that had showed signs of water
intrusion.
It’s important that the flashings used with
manufactured-stone veneer are wide enough to divert water out
and over the stone. The head flashing over this window was
custom-fabricated from 24-gauge G90 galvanized sheet metal with
a painted finish (800/231-8127, berridge .com). We pulled back the
StuccoWrap, applied a bedding sealant, and fastened the drip
cap in place (Figure 3).
Figure 3. To limit water and air infiltration, the
author applies a bed of sealant to the flashing tape above the
window (above), then installs the metal cap flashing
(right).
Before pulling the StuccoWrap back down, we attached a #36 weep
screed over the drip cap (Figure 4). This
screed is made from 26-gauge galvanized steel to meet FHA and
code requirements for stucco installation (2006 IBC 2512.1.2).
It has a 3 1/2-inch-wide flange and 1/2-inch-diameter holes in
the kickout at the base, which help disperse water flowing down
the drainage plane.
Figure 4. A metal weep screed above the window allows
water to drain out from behind the cladding and mortar base
coat (left). Metal J-mold is applied underneath the window
(middle) and at the jambs (right); flexible sealant is used to
fill the joints between the J-mold and the window.
At the jambs and bottom of the window, we fastened stucco
J-mold.
Next we stapled up two layers of 60-minute building paper
(Figure 5). At the base of the wall, we lapped
the paper over #7 weep screed, which is similar to #36 screed
except with a full V-profile at the ground. Then we installed
the galvanized metal lath.
Figure 5. Crew members install a double layer of
60-minute grade D building paper on top of the StuccoWrap
(above). The paper laps over a metal weep to allow for drainage
at the base of the wall (above right). Galvanized metal lath
(right) is then installed over the building paper.
After the masons applied the mortar base coat and finished
reinstalling the stone veneer, we came back and detailed the
joints between the window frame and the metal J-mold
(Figure 6). To prevent three-point adhesion,
we first filled the joint with backer rod, then applied #900
Solar Seal adhesive sealant (800/654-1042,
npcsealants.com), a solvent-based product
that cures even when the mortar is still damp (Figure
7).
Figure 6. Like stucco, manufactured-stone veneer is
applied over a base coat of mortar (left). The cap flashing
(right) is sized to match the thickness of the stone veneer, to
ensure that water is diverted to the surface.
Figure 7. Backer rod inserted between the metal J-mold
and the window frame (top left) prevents the sealant used to
fill the gap (top right) from adhering to the back of the
joint, allowing it to remain flexible without pulling away from
the sides. At bottom, the finished wall.
In the end, we didn’t have to replace any of the interior
drywall; by the time the exterior repair was completed, it had
dried out adequately. Also, damage to the framing and sheathing
turned out to be minimal. So, in a sense, the homeowners were
lucky: In another couple of years, there would have been
compost in the walls.
Still, the callback cost the builder $13,500 — a lot more
than if the installation had been correctly detailed in the
first place.
Builder Mark Parlee specializes in exterior renovations
and water-management details in Urbandale, Iowa.