Air distribution is the weak link in many heating and cooling
systems. Here's how the industry's top pros detail their ductwork
— for results you can take to the bank.
by Ted
CushmanExperts agree that sealing ducts is vital to good HVAC
performance, especially in a vented crawlspace or attic, where
leaky return ducts will continually draw moist unconditioned air
directly into the air handler. At around $6 a bucket,
high-performance duct mastic is cheap, but the labor to seal the
ductwork properly is tedious and painstaking.
Good ductwork is key to HVAC performance. Yet hidden away in the
dank crawlspace or the hot, humid attic, a home's ductwork goes
unappreciated and underexamined. And too often, sad to say, this
vital part of the HVAC system brings the energy perfor-mance of the
home to surprising lows.
In one study, for example, researchers with the Florida Solar
Energy Center (FSEC) replaced several oversized air conditioning
units with "correctly" sized machines that matched the house
cooling loads, as calculated according to the Air Conditioning
Contractors of America (ACCA) design standard, Manual J. In theory,
performance should have improved — but instead, the new
systems saved little if any energy, while the homes' indoor
humidity actually went up.
Why the disappointing results? Ductwork. When the researchers
installed the new equipment, they left the old ductwork in place in
the homes' roasting-hot attics. In operation, the new smaller units
tended to move a lower volume of air through the ducts, more
slowly, for longer run times. So the cold air was exposed to hot
attic conditions for longer — essentially wasting the
equipment's cooling power on what amounts to outdoor space (only
hotter). And leaks in the ductwork had more time to do their
damage: longer run times meant more cold air was sent into the
attic from supply duct leaks, while a greater volume of hot, humid
attic air got sucked into the home from return air leaks.
Ultimately, the new, supposedly "right-sized" air conditioners
couldn't provide comfort while fighting the unfavorable attic
conditions. (For the full report, see www.fsec.ucf.edu/en/publications/pdf/FSEC-CR-1641-06.pdf.)
The Florida results came as no surprise to Texas-based building
performance consultant Doug Garrett (www.bldgperformance.com).
"What happens to lots of people," says Garrett, "is they take out
their old SEER 7 or 8 system and put in a new SEER 14 or 16
machine, and they think that their bills are going to go down 50%.
But their bills only change, like, 5% — because there's a
mismatch between their duct system and the equipment's required
airflow. You can take a darn good piece of equipment and just
absolutely skewer it by putting it on an existing, crappy duct
system."
Supply Leaks
Leaks through supply ducts into unconditioned space may result in
negative pressure in the living space, causing unconditioned air to
be drawn into building cavities.
Terrible Is Typical
As it turns out, undersized duct systems with high-friction
fittings, major air leaks, excessive run lengths, and crippling
twists, kinks, and bends are the norm in the U.S., not the
exception. A 1994 Department of Energy study estimated that
nationwide, heating and cooling systems were operating at 60% of
the design airflow because of undersized ductwork. "I thought that
was an amazing result," notes Garrett. "But when I bought my own
flow hood and started measuring airflows, I found the same thing.
In my market, systems that are supposed to be 2,000 cfm — say
400 cfm per ton times five tons, for a five-ton system — I'm
measuring about 1,150 or 1,200 cfm in the return duct. That is
right at 60% of what it should be." Return ducts especially are
usually undersized, says Garrett: "When I go into a house, even
before I test the system, I'm already looking to see where I can
put the additional return capacity that I already know I'm going to
need."
Ordinary "duct tape" does not provide an effective seal because
heat, cold, and moisture will break the adhesive bond (left). Note,
too, the holes in the metal collar. This whole joint should get
mastic, then the liner and insulation should be secured by a
plastic compression tie. Ducts aren't the only source of leaks,
however. Below, a smoke gun shows where an air handler cabinet is
allowing air to enter the system from the unconditioned
attic.
Don Swift, the Technical and Quality Control Director for New
Jersey's Home Performance with Energy Star program, sees the same
pattern in his state. "Even in some fairly new homes, we see that
the duct systems are undersized and leaky. A typical duct system
here in New Jersey will lose 20% to 30% of the airflow to the
outside." And many New Jersey contractors still use wall cavities
as makeshift returns, says Swift. When system fans put the unsealed
cavities under negative pressure, the air conditioner sucks in
outdoor air via floor system voids that communicate with the
building's band-joist area. This leaves retrofit technicians with
no choice but to break open walls to install real ducts, or else
abandon the existing duct chases entirely and install new ducts (if
they can find space for doing that). Those repairs cost a lot more
than it would have cost to do the job correctly in the first place,
notes Swift. "That's why Energy Star's new homes program tries to
educate builders to do it right from the beginning — so we
don't keep creating these problems."
In Louisiana's hot, humid coastal climate, ductwork in the attic
can also cause moisture problems. Home-building consultant Paul
LaGrange says most HVAC contractors in his south Louisiana market
use flexible duct for their attic duct runs. Careless installation
practices often result in ducts being intertwined and tangled
around each other. "If the ducts touch each other, or touch
insulation, that contact surface becomes cool enough for moisture
in the attic air to condense on the duct," explains LaGrange. "From
July through October, my phone rings off the hook — people
saying that it's raining in their house. And you go there and you
realize that their ductwork is reaching the dew point. You stick
your hand in between two flex ducts, or between rigid duct and
blown insulation, and it comes out sopping wet. Water is dripping
over the insulation and through the gypsum board ceiling, because
the air conditioner is running all day and night and it is
constantly condensing and dripping."
Return Leaks
Leaks in an HVAC return can suck unconditioned air into the HVAC
system, increasing the cooling and humidity load, particularly if
the unconditioned air drawn in is excessively damp. The
unintentional airflows put the living space under a positive
pressure that can drive cool, conditioned air into the building
cavities. The same effect occurs when the return duct has been
undersized — an all-too-typical design flaw.
It's another case where bad ductwork can work against advanced
equipment, says Doug Garrett. "The advanced variable-speed systems,
the ones that have a dehumidification function — they slow
the fan speed down, and they do extra-good dehumidification. That
means that they put out extra-cold air, and so the ducts get extra
cold. On really high dew-point days, especially down there along
the coasts, I have seen all of the ducts in people's attics —
and I mean all of them, from the unit to the boot, every duct in
the attic — covered in water. You could not touch any part of
any ducts without water running down to your elbow." In one luxury
home, says Garrett, the executive owner "had little plastic buckets
under every supply grille in the 12,000-square-foot house, because
water was dripping out of the grilles. They thought the grilles
were condensing, but they weren't — every duct in the attic
was condensing, and the moisture was just running down to the
grilles."
Twisted, tangled flex duct not only slows airflow, but the
contact between the ducts
cools the contact surface and promotes harmful condensation on the
duct surface.
In that case, the repair was to insulate the attic ducts to higher
levels and to keep them isolated from each other and from any attic
insulation. And the hotter and more humid the climate, the more
insulation exposed air conditioning ductwork needs. In coastal
Louisiana's climate, notes Paul LaGrange, the International Energy
Conservation Code (IECC) calls for R-8 insulation liners on attic
flex duct — but the state legislature has stepped in to back
the requirement down to R-6. It's a marginal cost savings, says
LaGrange, but a surefire recipe for moisture problems.
Doing Ducts Right
In new construction, builders have the opportunity to start fresh,
with right-sized heating and cooling equipment and properly
designed, carefully installed ductwork. Good results do require
skill and attention. But with a systematic approach, success is
within reach.
Start with the house plans. Most house
plans make no allowance for ductwork, says Doug Garrett.
"Architects evidently are not aware that houses are heated and
cooled with forced-air systems. I sometimes think it would be front
page news in an architecture magazine if you ever informed them of
this. I have seen rooms 28 by 32 feet that have no way that you can
get a duct to them — like, with red iron in the way." Says
Brad Townsend, a building science manager with Masco Corporation's
Environments for Living program (www.eflbuilder.com): "People
design these buildings, and now the poor HVAC contractor has to
make his ducts fit around all this structural stuff. And sometimes,
there's just no way to get air from point A to point B." It can be
as basic as rightsizing a duct chase, explains Townsend. "Give the
contractor enough room in the chase to install the duct you need. A
lot of times, they'll restrict that flow with a 12-inch chase when
the guy needs to use a 16-inch duct. You're just setting yourself
up to fail."
Duct sealing and insulation are less critical when ductwork is
brought within the home's insulated envelope. Here, we see ducts in
a dropped hallway chase at the LaHouse project.
One solution employed in the LSU LaHouse demonstration home uses a
dropped chase in the central hallway, so that all the ductwork has
a place to run below the insulated attic floor, within the
conditioned space. This makes sealing and insulation less critical
(although sizing and airflow balancing remain as important as
ever).
For her "Not So Big" show house at the 2005 International Builders
Show in Orlando, Fla., nationally known residential architect Sarah
Susanka brought the ductwork inside the building envelope. She
placed the ducts within chases created by ceiling soffits running
around the room perimeters. In this case, the lowered ceiling
provides a distinctive design element that does double duty serving
a practical HVAC purpose.
Get the loads right. To make AC and
forced-air heat work, you need to calculate the heating and cooling
loads for the whole house, room by room. The right way to do this
is with ACCA Manual J. The latest version, Edition 8, accounts for
things like window area, dual low-E glazing, shading, and
orientation — not just insulation levels and room volume
— and the figuring gets too complicated to do by hand. A pro
HVAC contractor should have an ACCA-recognized computer program to
size systems — and he should know how to use it, without any
fudging or guesstimating.
Sarah Susanka's "Not So Big" show house in Orlando, Fla.,
features a soffit at the perimeter of most rooms. This provides
ample room for running ductwork and keeps those ducts inside the
building envelope. These chases also provide a key design element,
providing ceiling height variety that makes each room feel
larger.
Size the ducts accurately. Manual J
supplies room-by-room heating and cooling loads, and also specifies
the required airflows to handle the loads. Software packages also
let the user run a "Manual D" calculation with the click of a mouse
(Manual D is ACCA's duct design standard, a spinoff of Manual J).
But once you know the design airflow requirements, you don't have
to use Manual D — simple duct calculators, or "ductulators,"
can also provide good answers. However, you do need the right
ductulator for the material you're using — sheet metal ducts,
fiberglass duct board, and flex duct all allow different airflows
for a given diameter of duct. Relying on a ductulator calibrated
for sheet metal — the most common kind — for a job that
uses flex duct will give you ducts with only 70% of the needed
capacity, or less.
Flex duct needs proper support every 4 to 5 feet. A narrow
strap like this (top) chokes off the duct and reduces the airflow.
Good support should be provided by broad saddles or wide straps
(above), which allow air to flow through the ducts at their full
design capacity. For best results, contractors should test and
verify actual airflows after installing, then correct any
discrepancies.
Use short, straight, well-supported runs. Bends
create friction that slows the air down. Every 90-degree bend in a
duct adds the equivalent of 70 feet of duct length, reducing
airflow to the room the duct serves. If you have to turn a corner,
try to do it with two 45-degree bends instead of one right angle
— gentler angles or slow curves are less damaging. In any
case, every bend should be noted in the duct design program, so the
program can compensate by increasing duct diameter if need
be.
Just as a tight bend can inhibit airflow, poor support can cause
the duct to collapse and the few straps provided can choke off the
duct. Codes typically require support for flex duct at least every
4 to 5 feet.
Use low-friction fittings. Different
fittings have different air resistance characteristics. "All people
have to do is look on the back of their ductulators," says Doug
Garrett. A tee fitting, for instance, creates more drag than a wye.
And again, fitting choice should be fed back into the ductulator or
program to allow for adjustments.
Seal thoroughly. Leakage losses are the
biggest threat to duct performance — and the more friction in
the duct, the more air will escape through leaks instead of
reaching its intended destination. Codes allow either duct-sealing
mastic, or specialty tapes that meet the UL-181 standard from
United Laboratories. But some programs insist on the mastic,
arguing that mastic is more flexible, resilient, and durable than
tape.
While a UL-181 duct tape is allowed by code, best practice
calls for sealing ducts and fittings with mastic. Joints in metal
ducts should be reinforced with a fiberglass mesh tape (top).
Fittings should also be enshrouded in mastic. Duct tape has obvious
limitations for sealing the multiple penetrations in a metal duct
boot (middle), whereas mastic provides a lasting seal
(bottom).
Test and correct. Whatever design
program, duct material, and duct-sealing method you use, you can't
be sure what you have accomplished if you don't test. Only the top
professional contractors tend to be equipped with flow hoods and
duct blasters for measuring airflow and leakage, but those are the
contractors who can guarantee that they've done what they set out
to do. Says Brad Townsend, "There are ways to test these systems in
the rough, before I drywall, when I can still access everything.
Most furnaces run on 110 power. So I can plug into a generator,
install the grill, and attach my flow hood so I can capture and
measure that air in the rough." Top contractors, says Townsend,
leave themselves a little margin for error with their ductwork
sizing, and install adjustable dampers at the register so they can
make fine adjustments. That way, they can nail the design airflows
in the field, every time.
And in the production setting, Townsend points out, you only have
to figure things out once. "I'm going to build this model for the
next five years," he says, "and probably build several hundred of
them. Once I get this design, that structure's not going to change.
And I can get consistent and repeat that performance, over and
over." ~
Contributing editor Ted Cushman has been
covering construction business and technology since
1993.