Clayton
DeKorne
Q:
How do you detail a sealed crawlspace
for a flood zone? Do we have to insulate the floor, or can we just
insulate the crawlspace walls?
A:
Insulation in the floor is
inevitably interrupted by wires, pipes, ductwork, and bridging. In
a typical first floor, these interruptions make it next to
impossible to get a tight air seal, which is often a more critical
element to the energy and moisture performance of any building
enclosure than the R-value the insulation provides. But depending
on the flood zone, insulating the floor may be your only
option.
Open Foundations
The National Flood Insurance Program (NFIP) requires open
foundations in V zones and "strongly recommends" them in Coastal A
zones. An open pile or column foundation will diffuse the intense
force of a storm surge, allowing breaking waves to pass harmlessly
beneath the first floor of the home. In this case, the thermal and
air boundary of the house is defined by the first-floor framing.
But I've yet to see a really good floor insulation detail that
provides a tight air seal.
The best approach is to use foil-faced polyisocyanurate foam board
on the bottom of the joists. Tape the seams with foil tape, then
fill the joist cavity with unfaced fiberglass batts. To be
effective, the insulation should be installed without gaps or
compression and should be in full contact with the subfloor, which
will require filling the entire joist depth with insulation. Also,
some code jurisdiction may require the foam to be fire-rated or
protected with a noncombustible material, such as an exterior
gypsum sheathing.
Sealed Crawlspace Option
In areas outside the V zone and Coastal A zone that are subject to
ponding or low-velocity flows, floodproofing efforts center on
relieving hydrostatic loads on the crawlspace foundation, planning
for removal of floodwater and sediment from the crawlspace area,
elevating utilities, and using flood-resis-tant materials.
To relieve hydrostatic pressure on a stem-wall foundation, the NFIP
requires vents that allow water to flow through the stem wall.
While this suggests a vented crawlspace, it's possible to create a
sealed crawlspace using Smart Vent Flood Vents (www.smartvent.com).
These vents remain closed under ordinary conditions, but when
floodwaters rise, floats in the vents open a vent gate to alleviate
hydrostatic pressure of the water that might cave in the
foundation.
To build a sealed crawlspace, the best approach is to insulate the
walls with a water-impervious insulation such as a closed-cell
sprayed-in polyurethane or rigid extruded polystyrene (see
illustration). Key details for controlling moisture in the
crawlspace include covering the floor with heavy-duty poly sealed
with mastic and providing plenty of drainage.
For drainage, exterior footing drains are a must. Much better are
drains on both sides of the footing, connected across the footing
at the low corner. The crawlspace floor should slope to that low
corner, and a floor drain with a backwater valve should be
installed. The drain inlet gets covered by a grate that's sealed to
the poly with mastic. Ideally, the high point of grade below the
crawlspace would be above the surrounding grade, with the drain at
or above the exterior grade height. If the crawlspace floor is
below the surrounding grade, code requires dampproofing on the
crawlspace walls.
Joints in the poly must be "shingled," but in this case the sheets
must be lapped to shed water beneath the poly. This means the laps
are reversed from the way it would be done for roofing
underlayment. If the sheet is lapped the right way, it will allow
the water underneath to flow past the joint, but if the sheet is
lapped the other way, it will scoop water and hold it against the
mastic seam.
In termite country, the foundation insulation must be kept a couple
of inches below the top of the foundation to create a clear area of
masonry. This gap will allow for inspection, and if termites do
invade, they must be dealt with using soil treatments or baiting
systems (see "Keeping Termites at Bay," Summer 2005; available
online at www.coastalcontractor.net).
A sealed crawlspace is designed to bring the crawlspace area inside
the conditioned space. To make this work, Jeff Tooley, a North
Carolina contractor whose Healthy Building Company often takes on
problem crawlspaces, prefers to actively condition the space with a
dedicated, low-sone fan rated for continuous duty. Tooley typically
installs the fan under the floor 8 or 10 feet away from a floor
register, connected by a run of flex. Separating the register and
the fan in this way makes for quieter operation. Other builders are
content to passively condition this space with open floor registers
to ensure that the air in the crawlspace and living areas
"communicates." In either case, the goal is to maintain the
crawlspace at humidity levels roughly the same as the main living
areas of the house.
The sealed crawlspace approach takes care of the day-to-day
moisture and energy issues in the crawlspace. In the remote chance
a flood occurs, it's likely the drainage will be overwhelmed and
the crawlspace will fill up like a bathtub. However, if
flood-resistant materials are used (plastic insulation and
masonry), the crawlspace can be pumped dry without lasting harm. In
this case, the poly covering the floor may be covered in sediment,
which could contain wastes and other toxic materials that you would
not want to leave under the house, and will need to be replaced.
— Clayton DeKorne