by Clayton
DeKorne
Soak a chunk of stucco from a demolition project in a bucket of
water. You can leave it there for days, and some water may seep
through the cold joints between the three layers at the broken
edges, but the core will stay dry.
This is the lesson an old-time plasterer taught me about stucco.
Done well, stucco is impervious to water. But this is not exactly
the emphasis Joe Lstiburek of Building Science Corp. put in his
report to the Florida Home Builders Association following the 2004
hurricane season. After examining the extensive water damage to
homes from more than 20 inches of rain washing over central Florida
when Hurricanes Charlie, Frances, Ivan, and Jeanne swept across the
state, Building Science Corp. searched for the leakage pathways by
simulating weather conditions with spray racks and pressure
washers. The result of this investigation was no real surprise to
Lstiburek: "Stucco claddings leak [as do all claddings]." Lstiburek
does not dispute that, as a material, stucco without cracks is
impervious to water. But cracks are inevitable in real-world
buildings, leading to the company's critical conclusion: "Based on
the field observations, it is our belief that it is not possible to
construct stucco assemblies without cracks."
It's hard to argue with conclusions based on actual site
conditions. Facing the certainty of leaks, Lstiburek's
recommendations rightly focus on creating "drainable assemblies,"
using flashings and water-resistive barriers, and on details that
ensure that when water is forced into a wall, it has someplace safe
to drain away and a means by which the wall can dry out. His report
(www.buildingscience.com/resources/walls/rainwater_management.pdf)
is a must-read for anyone using stucco in any environment but
particularly in hurricane-prone coastal regions.
Heartbreaking Reality
At the same time, Lstiburek's report is disheartening. It
underscores the fact that good three-coat stucco seems completely
absent on the ground in central Florida, and I doubt Florida is the
only state where the practical realities of schedules and budgets
push contractors toward alternatives to traditional three-coat
systems.
Lstiburek's report lumps three-coat stucco with "cementitious
decorative finishes" — often known as one-coat systems. This
was not a lapse on the part of Building Science Corp. but rather a
deliberate move to address what's actually used in the field. In
the end, Lstiburek wrote by e-mail, it doesn't matter if it's a
one-coat or a three-coat system. Both types are subject to
cracking; both types fail.
That's the heartbreaking part, because three-coat stucco, by
design, ought to be much more resilient to moisture than a one-coat
system. A well-applied three-coat system creates three layers that
act independently. This cannot eliminate cracking, but it will
largely reduce the chance shrinkage cracks in each of the three
layers will communicate the leak all the way through the
wall.
"We've known for a long time how to keep water out," says Ron
Webber, president of the Plastering Contractors Association of
Southern California and a plastering contractor for more than 30
years. Webber underwrote testing in the mid-1990s with Michael
Roberts, a stucco expert in Orange, Calif., to address extreme
cracking problems with stucco occurring all too frequently on
sites. The work set out to evaluate the shortcuts taken by some
stucco applicators to make a batch of wet mud easier to spread on a
wall. These include the use of clay fines mixed into the sand to
make the mud buttery, lime to fluff it up, and soap to smooth it
out. All three practices, Webber confirmed, reduce the strength and
water resistance of stucco.
Old-School Stucco
Unlike concrete, which is designed to be as strong in compression
as possible, stucco is designed to maximize tensile strength,
explains Webber. This is no small trick, as stucco's not a material
naturally strong in tension. Key steps include the following:
Solid structure. A wall is only as strong
as the foundation below it and the ground beneath that. Begin with
well-drained, properly compacted soil that has the capacity to
support the structure above it. The wall itself must be rigid;
stucco can't tolerate movement. If well reinforced, and the top
floors, roofs, and gable ends framed in wood are well anchored to
the basewalls, block construction makes inherent sense in a coastal
environment. "It's unclear if any wood framing system can ever be
rigid enough and dimensionally stable enough to keep stucco from
cracking in humid, high-wind regions," says Webber. "Block walls
are much more stable and structural cracking much more
controllable."
A wood-framed wall stiff enough for high-wind zones requires
tightly nailed APA-rated plywood sheathing. OSB, while structurally
equivalent, will take longer to get wet if exposed to water, but it
will swell, particularly at the edges, and it stays swollen after
the panel has dried. If this happens before the stucco gets
applied, it may create irregularities in the surface that the
plasterer will feel obliged to flatten out to make his work look
good. The result is thin spots in the stucco that are prone to
cracking.
Drywall first. In a wood-framed
structure, drywall must be hung before the lath and scratch coat
are applied. The weight of drywall will stress wood framing,
causing early settlement cracks, which can be acute if the drywall
is hung before the scratch coat has hardened. Avoiding such
problems, however, often comes down to a schedule that is easier to
set than it is to stick to.
Lath. Block walls do not typically
require lath. The surface should be clean and sufficiently damp and
rough to ensure a proper bond. But block surfaces vary widely, and
not all block bonds well to stucco. Webber always does a test patch
to test bond strength. If he's not satisfied, he'll use a bonding
agent or apply a Portland cement dash coat of one-and-a-half parts
sand to one part Portland cement, then test again. If still not
satisfied, he'll apply metal lath to the block.
Metal mesh must be installed with the right side up, or the stucco
will slide off the building. At corners, make sure that the lath is
not installed too tightly, or the stucco will pop off. Use corner
bead for best results (Figure 1). On wood framing, lath must be
installed with the long dimension perpendicular to studs. Best
practice calls for securing lath with furring nails, which place
the lath in the center of the scratch coat. However, the norm over
wood framing has moved toward pneumatic staples, which push the
lath hard to the structure, limiting its effectiveness.
FiGURE 1. CORNER BEAD. To prevent stucco from
popping off at outside corners, use corner bead. An alternative
(not shown) is to round the corner, allowing the lath to pooch out
and provide plenty of room for stucco to key to the lath. The end
result is a rounded corner that may not be compatible with all
architectural styles.
Clean sand is the key to creating a
strong coat, with either traditional three-coat or one-coat
materials (Figure 2). Webber urges all stucco subs to provide
verification to builders that they are using sand that conforms to
ASTM 897 for gradation and has a minimum SE (sand equivalent)
rating of 70. The SE is a designation of the amount of fines in the
sand. "Dirty" sand, or sand intentionally mixed with clay to
improve workability, will become porous as the clay dissolves,
leaving behind air pockets.
FIGURE 2. CLEAN SANDis as important
to stucco as a low water-to-cement ratio and dry cement. "Dirty"
sand, or sand intentionally mixed with clay to improve workability,
will become porous as the clay dissolves, leaving behind air
pockets. In humid climates, watch out for older bags of cement.
Humidity can partially react with the cement even if the bags have
never been opened.
One-coat mixes are suspect, as well. The code allows "up to 10%
other materials," Webber reports, but because one-coat systems are
proprietary, it's not clear what's in that added 10%. Webber
suggests that additives may include surfactants that not only lower
strength but also reduce the surface tension of water, making it
slippery enough to slide through the smallest pore in a permeable
weather barrier. Surfactant compounds include the soap sometimes
added by applicators to improve workability.
Scratch coat. The first coat serves as
the foundation for the next two coats. It should be harder than the
brown coat and requires a richer mix — one part cement to two
to four parts sand. Webber recommends Type II cement without lime
or other additives. "It's got no body and is hard to spread, but
when cured, is super strong," he says (Figure 3).
FIGURE 3. SCRATCH COAT.The first
coat should be the hardest, using a rich mix. Stucco contractor Ron
Webber recommends a Type II "plastic" cement without lime or other
additives for the scratch coat. The mix will have no body and is
hard to spread, but applying it with a pump makes this practical
and results in the strongest possible base coat.
Before applying the brown coat, Webber verifies the hardness of the
scratch coat by dragging a nail over the wall. If the nail does not
dig in but leaves a white line, the stucco is hard enough for the
brown coat.
Brown coat. This is a leveling coat that
provides the flat surface for the finished wall. The brown coat
also adds strength and thickness, and it is in large part what
determines the quality of the finish. It's a little sandier, at one
part cement to three to five parts sand. The increased sand helps
reduce the number of shrinkage cracks.
Finish coat. This is what provides the
final texture and color (Figure 4). Premixed finish-coat materials
usually work fine. Webber recommends steering clear of dark colors,
especially reds. Dark colors are prone to spottiness and, if not
well blended, will not match the color sample.
FIGURE 4. FINISH COAT. Code requires waiting
at least seven days before applying a finish coat. Hairline cracks
in this color coat are inevitable, but if the base coats are well
cured, these surface cracks will not communicate water through the
stucco.
Curing. By code, builders should provide
at least 48 hours of curing time after the first coat is applied
and wait seven days after the second coat before applying the
finish. The critical consideration is that the scratch coat must be
hard.
Curing schedules, however, prove to be
the Achilles' heel of modern-day stucco. The first and second coats
are often installed in the same day to keep the stucco crew on the
job site. Except on a handful of custom jobs, it's rare for the end
of the job to wait seven days in a fast-paced construction climate.
Such are the realities that push Lstiburek to his hard-lined
conclusions.
Managing Water
Ultimately, leaks do not matter, Lstiburek contends, if the wall
functions as a "drained assembly." Leaks do matter if the wall
functions as a "mass assembly," he continues, but the water getting
past the stucco can still be managed to avoid problems.
Drained assembly, in this case, refers specifically
to stucco over a water-resistive barrier, such as housewrap,
asphalt felt, or Grade-D building paper, applied over wood framing.
In the western U.S., building codes have caught on to the fact that
stucco needs two layers of paper, not just one, to create an
effective drainage space, yet such a rule doesn't apply in most
coastal jurisdictions. Stucco tends to bond to housewrap and
building paper. Without a bond breaker — a second layer to
separate the stucco from the weather barrier — water will
move right through any permeable membrane. Using paper-backed lath
over a housewrap or felt saves time over installing three layers
— housewrap, bond breaker, and lath — before stucco can
be applied.
Mass assembly refers to a wall made of
materials that are not affected by water, like a concrete block
coated with stucco. This wall has the capacity to store a lot of
water, however. Lstiburek contends that whether intended to work
this way or not, once you accept that leaks are unavoidable, this
is how a block wall functions. Its water-holding capacity is based
on a "rate-storage" relationship. When the rate of wetting exceeds
the rate of drying, moisture accumulates in a mass wall. As walls
become saturated, as many did in the extreme conditions of the 2004
hurricane season, water soaks through to the inside.
To prevent the water absorbed by a mass assembly from damaging
interior materials, Lstiburek recommends forming a stepped-down
shelf at the slab edge, strapping interior walls over foam to
isolate drywall from the wet wall, and installing a weep screed at
the bottom edge of the stucco to allow accumulated water to drain,
as shown above (Figure 5). Particularly important is proper
detailing for a control joint required where wood-framed walls meet
masonry basewalls (Figure 6).
FIGURE 5. MASONRY WALL DETAILS. To manage
water that builds up in a leaky block wall, form a step in the
foundation edge to direct water that reaches the base of the wall
outward, rather than allowing it to seep inside, where it can
damage flooring. Isolate a potentially wet masonry wall from
interior drywall with a continuous layer of semipermeable foam,
such as extruded polystyrene (EPS) and strapping. EPS foam, rather
than more impermeable XPS or polyisocyanurate, will allow the wall
to dry to both the inside and the outside over time.
FIGURE 6. CONTROL JOINT. Where wood-framed
upper walls meet masonry basewalls, code allows a metal expansion
joint applied on top of the weather barrier — a detail that
allows water that gets past stucco to drain into the basewall. To
create a true drainable assembly, flash the joint with a
peel-and-stick membrane (A), then apply a weep screed (B). Bring
the upper-story weather barrier (C) over the top leg of the weep
screed, then apply paper-backed lath, (D) which provides both a
bond breaker and reinforcement for the scratch coat.
Lstiburek acknowledges in his report that "Workmanship, quality
control, and cure impact the number and extent of shrinkage
cracking. Soil conditions, the nature of the materials, geometry,
and aspect ratio of mass wall assemblies impact the number and
extent of settlement cracking." However, in the end, he urges that
despite efforts to control these variables, a builder should expect
shrinkage and settlement cracks, and plan to deal with the water in
other ways. Regrettably, that's our practical reality. ~
Clayton DeKorneis editor of Coastal
Contractor.
Photos by Ron Webber except where noted.