- Q.My clients want to install
a built-in high-Btu gas griller as part of a planned
outdoor kitchen on the deck attached to their house.
Can the cooker be placed under a protective overhang
created by extending the existing roof?
A.Mike
Casey, a licensed plumbing and general
contractor and ICC-certified building inspector,
responds: When it comes to outdoor cooking
areas, the IRC is not too specific about
clearances, placement, and ventilation requirements
for gas appliances except to advise that
installations should follow the
manufacturer’s instructions. Code is also
a bit confusing regarding vertical clearance to
combustibles above broiler and range units. For
example, Section M1901 of the 2006 IRC requires 30
inches of vertical clearance for ranges, while
Section M1505 requires a metal exhaust hood above
an open-top broiler and at least 24 inches of
vertical clearance to combustibles. No distinction
is made between interior and exterior
installations.
Manufacturers may have additional requirements.
For example, Viking requires 6 inches of minimum
clearance to combustible sidewalls for its built-in
gas (propane or natural) outdoor range tops,
wok/cookers, and grillers, and specifies that these
models can’t be placed “under an
overhead that is unprotected and
combustible.” In my opinion, this would
clearly rule out the kind of installation you
describe, but your local building official might
allow it if the combustible material is protected
and other clearance requirements are met, or if a
noncombustible hood is installed above the
appliance.
My recommendation is to research the style and
brand to be installed, consult the installation
instructions for specific clearances and location
restrictions, and then contact your local building
official for an interpretation as to where and how
the unit can be installed.