- Q.Are there any
special requirements for electrical grounding when
using metal studs?
A.Redwood Kardon
responds: Wherever steel studs are used to
support NMC cable (the plastic-jacketed cable
commonly used in residential construction), there
is the potential for the framing to become
energized. Metal electrical boxes or metal
equipment that might be attached to steel studs
must always be grounded, which effectively grounds
the studs. When plastic device boxes are used, I
recommend installing a bonding jumper to the steel
frame. This jumper should be sized to match the
highest-rated breaker that feeds the specific
section of wall. In some areas, the electrical
inspector may require a bonding jumper for steel
boxes as well.
While the National Electric Code (NEC)
does not specifically address the question of
grounding a steel frame in residential
construction, Section 250 of the NEC
contains two citations that mention "structural
metal frame of a building" as applied to large
steel structures. Section 250-58a says the metal
frame must not be used as the equipment grounding
conductor for alternating-current equipment. The
intent here is to make sure that any electrical
faults are directed to the equipment grounding
conductor — not through an unreliable path
like the steel beams or studs.
Section 250-81b says the metal frame must be
part of the Grounding Electrode System (GES) when
the frame is intentionally grounded. The GES
primarily provides an alternate path for external
voltages (lightning and utility surges) so they do
not find their way through the structure. In
residential construction, steel studs are often
used in conjunction with wooden laminated beams or
treated wood mudsills, both of which act to isolate
the steel frame. But if the entire structure is
framed in metal and lightning is a significant
threat, then the structure should be effectively
bonded to the GES. (For more information on
lightning requirements, refer to National Fire
Protection Association publication 780-1992 [ANSI]
and check with your local jurisdiction.)
Redwood Kardon is a building
inspector in Oakland, Calif.