- Q.There are no code
requirements for smoke detectors in my area. What is
the best type of smoke detector to buy, and where
should they be located?
A.Art Laurenson, a
Providence, R.I., firefighter and assistant deputy
state fire marshal, responds: To be sure you
are complying with local regulations, contact your
local electrical inspector and the local fire
department. For new construction, BOCA and NFPA 70
(the National Electrical Code) both
require hard-wired, interconnected devices with
battery back-up.
Residential smoke alarms should be wired on a
dedicated circuit. It’s a good idea to
have at least one light or receptacle-on the same
circuit, to alert the homeowners in case the
circuit breaker ever trips. Interconnected alarms
are usually wired in a daisy chain, using 14-3 or
12-3 cable. The third conductor is the
communication wire.
Some installation guidelines:
- As a minimum, one device is required on
every occupiable level of the house.
- At wall-ceiling intersections, there tends
to be a dead space where smoke doesn’t
accumulate, so smoke detectors
shouldn’t be located in corners. While
smoke-detector manufacturers allow the devices
to be located as close as 4 inches to the
wall-ceiling intersection, some codes require
that a ceiling-mounted smoke detector be
located at least 12 inches from a wall and that
the top of a wall-mounted smoke detector be
located 6 to 8 inches from the ceiling.
- Install a separate smoke detector in each
bedroom and one in the common hallway near the
bedrooms.
- In most cases, a smoke detector should not
be located in a kitchen. The best device for
use near a kitchen is a smoke detector with a
hush mechanism, like the Firex model 4518 or
4618 (Maple Chase Co., 800/951-5526;
www.maplechase.com) or the First Alert model
4120 SB (800/323-9005; www.firstalert.com). The
hush mechanism disables the alarm circuit while
keeping the sensing circuit active. If the
amount of smoke continues to increase, the
device will sound again.
- An attic accessible by stairs (as opposed
to a ladder) needs a smoke detector. Although
NFPA 70 exempts unfinished attics, an attic
with stairs might be used by children to play
in.
- A basement is considered an occupiable
level and requires a smoke detector. If the
stair is open (with no walls), the smoke
detector should be installed at the top of the
stairs. If the stair is closed (with walls on
both sides), the smoke detector should be
installed at the basement ceiling near the
bottom of the stairs.
- Although not required by most codes, added
protection can be achieved by installing a heat
detector near the furnace or boiler and in the
garage. These heat detectors should be
interconnected with the house smoke
detectors.
- Large houses may need additional smoke
detectors. Some codes require one smoke
detector for every 1,200 square feet.