A.Paul Fisette
responds: As your own experience suggests,
unvented crawlspaces pose no real problems
— as long as there isn’t
excessive moisture. In your case, you have provided
a continuous sealed vapor barrier across the
crawlspace floor and, I would guess, proper
foundation drainage on the outside.
Nevertheless, you still have two code hoops to
jump through: the Model Energy Code and
the BOCA code. Unfortunately, in this case, the two
codes don’t necessarily jibe.
The Model Energy Code tells you how
much insulation you need and where and how to use
it to define the thermal envelope that protects the
"conditioned space" in a home. (To qualify as
conditioned, the temperature within the space must
be maintained at 50°F or higher.) The 1995
MEC (602.2.5) allows for an unvented
crawlspace as long as the perimeter insulation
meets a specified value. However, your design
appears to define the thermal envelope twice. You
should insulate either the floor of the living
space or the walls of the crawlspace, but not both.
If you remove the R-19 batts from the crawlspace
ceiling and upgrade the exterior foam as needed,
you could convert your "unconditioned" crawlspace
into "conditioned" space, and treat it like any
other conditioned space in the house where venting
is not required.
But then there’s the BOCA code. The
bottom line is, unvented crawlspaces are not
allowed under BOCA. Section 1210.2 treats
crawlspaces as "special spaces," and requires that
they be ventilated by either natural or mechanical
means.
Still, given your track record, you might be
able to convince your inspector to treat your
conditioned space the same as a basement, which
would typically not require any special ventilation
measures. If the inspector disagrees, you still
have a few options. You can get an engineer to
review your plan, deem it acceptable, and stamp it
to certify that it will perform as intended. This
seems like the most practical approach. You could
also install a mechanical exhaust system in the
crawlspace that is governed by a humidistat. This
may satisfy the code, but using an exhaust fan in
the crawlspace could draw moisture and radon into
the crawlspace. And lastly, don’t forget
that you have the right of appeal. You can petition
your state building officials to review the code as
it relates to your specific case. Refer to the code
commentary (your code official might have this),
which discusses the line of reasoning that went
into the development of this particular code
provision. If you can prove that your building
system works and does not violate the intent of the
code, you have a shot at gaining an approval.
Paul Fisette is director of the
Building Materials and Wood Technology program at
the University of Massachusetts in
Amherst.