by John Carroll
When leaks occur around a chimney, it's often
assumed that the roof flashing is at fault. But quite often the
problem is higher up. If a chimney is very old or poorly built,
with visible voids in the mortar joints, water can enter
through the masonry. It's more likely, though, that the cap is
the culprit.
Such was the case with a leaking 19-year-old chimney that I was
recently asked to repair. When I got up on the roof to take a
close look, I found the usual problems: The featheredged mortar
around the perimeter of the cap had weathered away, and cracks
had formed in the rest of the cap. These cracks probably
started the day the mason slathered on wet mortar to form the
cap (see Figure 1). As the mortar dried, the cap undoubtedly
developed shrinkage cracks, allowing small amounts of water to
penetrate the cap virtually from the moment it was built.
Though fast and easy to build, a mortared
chimney cap soon develops shrinkage cracks that allow water to
penetrate into the chimney, leading to leaks and
deterioration.
Differential movement between the cap and the flue liner may
have contributed to the cracks, too. Heat going up a flue
causes it to expand slightly, and with nothing to break the
bond between the flue liner and the cap, this upward thrust can
make a cap crack (see "Sleuthing for Chimney Leaks,").
Also, this particular chimney was missing one section of flue
liner. Apparently, the original mason ran short when he was
building the chimney, because he used brick to finish the last
8 inches of the flue. In addition to being a code violation,
this created a flat area on top of the bricks where water could
pool (Figure 2). And, without a flue liner projecting above the
cap, there was nothing upon which to clamp a metal flue cap and
screen. These components aren't always needed, but in this
case, birds or squirrels had at some point taken up residence
in the chimney; in an effort to keep them out, a previous owner
had inserted a wooden bracket so that he could install a metal
flue cap and screen. Because the present homeowner was unaware
of the wooden bracket, this modification turned out to be a
pretty serious fire hazard. The fact that the masonry cap
leaked, therefore, may have been a blessing in disguise (Figure
3).
Figure 2.Instead of ending with a clay tile
extending above the chimney cap, this flue was finished with
brick, a code violation.
Figure 3.A previous owner had inserted a wood
bracket into the top of the original chimney, creating a
potential fire hazard.
Build Cheap, or Build to Last
Building a cap to Masonry Institute of America (MIA) and Brick
Industry Association (BIA) standards adds several hundred
dollars to the cost of a chimney and ties up a mason's
scaffolding for several days (Figure 4). It's faster and
cheaper to simply apply a 2-inch-thick layer of mortar around
the flue liner and taper it down to a featheredge at the
outside of the chimney. That way, the mason not only uses up
his mortar and finishes the chimney in one step, but he can
begin taking down his scaffolding an hour or so after laying
his final brick. There is an undeniable short-term economy to
this method, but over the long haul such a cap is bound to
fail. Properly built, the cap should last the life of the
chimney, not just a decade or two.
Figure 4.Built of concrete rather than mortar for
durability, this industry-recommended chimney-cap design
features a small gap around the flue that allows it to move
independently of the cap when it heats up and
expands.
Fortunately, the design of the new cap in this project would
eliminate the major defects of the failed cap. I began by
setting up scaffolding that surrounded the chimney about 3 feet
below the top, creating a safe and comfortable working height.
Working from the scaffold, I used a grinder, hammer, and chisel
to remove the three brick courses that made up the final 8
inches of the flue. I also ground away the featheredge around
the perimeter of the existing cap. With a flashlight, I
carefully inspected the rest of the flue liner, finding it to
be in very good shape (Figure 5).
Figure 5.To prepare the chimney for a new cap, the
author removed enough bricks to expose the top of the last clay
tile and ground away the remnants of the old chimney
cap.
Next, I cut and installed a flue liner to replace the brick I
had removed. Using a 4 1/2-inch grinder equipped with a
dry-cutting diamond blade, I cut the flue liner down so that
about 9 inches of the flue would extend above the top course of
bricks on the chimney. The concrete cap would be 2 1/2 inches
thick around its perimeter and slope up toward the flue, with a
rise of about 3 1/2 inches, leaving roughly 3 inches of flue
extending above the finished cap.
I used refractory mortar to join the new flue liner to the old.
To hold the liner in place, I used columns of mortar. Industry
literature calls for a 1-inch air space between the flue liner
and the structure of the chimney, but most codes also require
that the flue lining be supported on all sides. To achieve this
contradictory goal, the IRC states that "only enough mortar
shall be used to make the joint and hold the liners in
position." The columns of mortar were what I deemed sufficient
to hold the liner in place (Figure 6).
Figure 6.Supported by columns of mortar, the new
clay tile extends 9 inches above the level of the chimney,
leaving plenty of room to accommodate the thickness of the new
concrete cap.
After letting the mortar columns set overnight, I filled the
spaces around the flue liner with sand. Since the entire flue
liner was already thoroughly encased in the masonry structure
below this final piece of the liner, I was not terribly worried
about the air space for the last 8 inches below the cap. I
filled it with sand to keep the concrete from the cap from
filling the space around the flue. This allowed me to hold the
flue in place while accommodating any slight upward movement of
the flue liner through the cap. If the chimney had had a
functional air space surrounding the flue, I could have used
sheet metal or tile backerboard to cover the gap on top.
Forming the Cap
The form for the concrete cap consisted of two layers. The
first, made of 2x4s, created a ledge that would cause the
concrete to extend 1 1/2 inches past the top course of bricks.
I installed this layer of the form so that it was even with the
top outside edge of the final course of bricks. Because I was
working alone, I used bar clamps to position and hold the
pieces initially, then tied them together with 3-inch deck
screws.
The second layer of the form, made of scrap 2x6s and 2x8s,
formed the outside edge of the cap. To give the cap a
substantial 2 1/2-inch thickness around its perimeter, I set
the top of this layer 2 1/2 inches above the top of the inner
layer of the form. Once again, I used clamps to hold the pieces
in place while I secured them with screws. Because I was
careful to cut and fit the pieces of the form tightly, it held
fast to the chimney by friction alone when I was finished. If I
had not been satisfied that the form would stay put, I could
have used my bar clamps to hold it in place.
A bond break is important. My
next step was to wrap the flue with foil-faced bubble-pack
insulation. Approximately 1/4 inch thick, inflammable, and easy
to wrap around the flue liner, this product is the best I've
found for isolating the concrete cap from the flue. It has
enough body to hold back the concrete during the pour, yet
contains air spaces that allow for differential movement
between the cap and the flue (Figure 7).
Figure 7.A double layer of 2-by material was used
to build a tightfitting form around the chimney. To create a
bond break between the flue and the concrete cap, the author
wrapped the clay tile with thin insulation. Sand fills the gap
around the flue while allowing for differential
movement.
Because the surface of the brick was irregular, I was concerned
about the form leaking when I filled it with concrete. I didn't
like the idea of wet concrete running down the outside face of
the chimney, so I caulked this seam with clear silicone caulk.
To reinforce the concrete, I cut and installed 6-by-6 welded
wire. I also installed 3/8-inch-by-3/8-inch strips of wood on
top of the inner layer of the form to create a drip channel on
the bottom of the cap overhang (Figure 8). To make it easier to
remove these strips after the concrete cured, I rubbed paraffin
wax on them.
Figure 8.Wire mesh was used to reinforce the
concrete; small 3/8-inch-square strips of wood placed in the
bottom of the form created a drip edge in the concrete cap
after the form was removed.
A stiff mix of colored
concrete. The next day, I poured the concrete cap.
Because I wanted the concrete to blend in with the chimney and
the roof, I mixed in a reddish brown dye while adding just
enough water to thoroughly hydrate the concrete, so that it had
almost no slump (Figure 9). The concrete was, in fact, so stiff
that it had to be pushed and pounded into place. But the
stiffness prevented it from running over or through the form,
and allowed me to form, stack, and shape the cap by hand. Also,
because the mixture was so dry, there was very little
shrinkage; as a result, no shrinkage cracks developed as the
concrete cured.
Figure 9.Dyed to match the color of the roof
shingles, the concrete used to form the cap had virtually no
slump, which minimized shrinkage during curing and made it
possible to push the concrete into shape.
My goal in forming the cap was to create straight, flat planes
that rose from each side of the form to a point about 3 inches
below the top of the flue liner. I wanted the intersection of
these planes to form straight lines, much like the hips on a
hip roof. I used hand floats to push the material into place;
by lightly rubbing the surface in a circular motion, I was able
to knock down the high points and fill in the low points. I
used two floats at once to get a crisp line along the hips. At
this point, my objective was to get the shape right. I wanted
the surfaces to be flat and straight, but because I wasn't
trying to make it perfect I did everything by eye (Figure
10).
Chimney flashing is a simple barrier; if it's
defective, water usually flows immediately into the
house. Water that goes through the cap, on the other
hand, is often absorbed by the mass of the masonry. In
many cases, it takes a lot of water and a lot of time
before the masonry gets sufficiently saturated to cause
problems. A saturated chimney, furthermore, can
continue to give up water after the rain stops. So, if
the owner reports that the chimney seems to leak hours
after the rain has stopped, I strongly suspect the cap
is the culprit.
When I inspect the chimney, I check out the roof deck
from the attic, if possible. If the area next to the
chimney is wet or has water stains, mildew, rot, or
other signs of prior leaks, water has most likely
flowed through a defect in the flashing. When I get up
on the roof, I look for obvious entry points for
moisture: cracks in caulk joints in the flashing;
missing or loose pieces of flashing; holes or cracks in
mortar joints; and cracks, dips, and deterioration in
the cap.
I also look for efflorescence, a white, powdery film
sometimes found on the face of brickwork. It occurs
when large amounts of water penetrate the surface of
masonry structures and dissolve salts present in the
bricks and mortar. The moisture carries these salts to
the surface and deposits them there. When the rain
stops and the surface dries out, the salt appears in
the form of a telltale white powder. Thus,
efflorescence above the flashing is a strong indication
that water is entering the chimney through the masonry
above the flashing.
When this detective work does not produce a clear-cut
suspect for the leaks, I try to find the problem
through the process of elimination. If the chimney can
be left unused for several weeks, I drape a tarp over
it and use a rope to hold it in place. This protects
the cap and most of the masonry above the flashing. So,
if the chimney continues to leak, I know it's the
flashing. If no leaks occur after several long, heavy
storms, I conclude that the trouble is in the masonry
above the flashing. In these cases, a deteriorating cap
is almost always the problem. |
Figure 10.To create the hips of the chimney cap,
the author used two floats. He pushed the concrete into
position and smoothed out high and low spots so that the cap
would easily drain water away from the flue.
Cure slowly for best results.
When I finished shaping the cap, I turned my attention to the
proper curing of the concrete. Hydration — the chemical
reaction that takes place when concrete cures — requires
water, and it's essential to keep concrete from drying out
prematurely. Therefore, I began by setting a couple of sheets
of plywood on the top of the flue to get the concrete out of
the sun. The temperature was in the 90s and the sun was shining
brightly, but this measure kept the concrete in the shade for
the rest of the afternoon. That evening, after the initial set
of the concrete, I covered the cap with wet burlap. Then I
covered the wet burlap with plastic and used two bar clamps to
hold the plastic in place. The next night, I removed the
plastic, soaked the burlap with water, then replaced the
plastic. I repeated this routine each day for three days to
make sure the concrete stayed damp for 72 hours (Figure
11).
Figure 11.Plywood placed on top of the flue
prevented the hot sun from accelerating the cure of the newly
poured concrete cap (top). After the initial set, the author
covered the cap with wet burlap (bottom left), then wrapped the
top with plastic held in place with bar clamps (bottom right),
a procedure repeated for three successive nights to promote
After the concrete cured, I removed the forms and did some
final work on the surface of the concrete. I began by mixing up
a rich slurry made of 50 percent portland cement and 50 percent
sand, using enough water to make it the consistency of wet
grits. I also added dye to make this concoction the same color
as the concrete, then rubbed it into the surface of the
concrete with a Carborundum rubbing stone. In this way, I
filled in the honeycombs and knocked down rough edges and high
spots (Figure 12).
Figure 12.Rubbed with a colored cement-and-sand
slurry that was applied with an abrasive stone, the finished
chimney cap has a textured finish. It should last as long as
the chimney it protects.
The next day, I cut the aluminum insulation so that it was even
with the top of the cap and pushed the top edge of it down into
the crevice between the flue and the cap. Then I filled the
joint with a gray silicone sealant to complete the job.
John Carrollis a mason and builder in Durham,
N.C.