In my 30-plus years as a plumbing contractor, I’ve
replaced countless water heaters. Our company, which works in
the San Francisco Bay area, installs three basic kinds:
conventional gas models, tankless models, and —
increasingly — condensing storage heaters. Customers who
want to save energy nearly always ask for a tankless water
heater. That’s no surprise — tankless heaters have
been getting a lot of media coverage and are the only efficient
heaters most people have heard of.
In most cases, however, we recommend condensing storage
heaters to our replacement customers, because they are arguably
more efficient than tankless models and — when used to
replace an existing heater — frequently less expensive to
install. For homeowners, switching from a conventional heater
to a condensing model is not a big change. If they consume the
same amount of hot water as before, they’ll have lower
gas bills and run out of hot water less often. Switching to a
tankless heater, by contrast, requires some lifestyle
adjustments: The homeowners will have to wait for the heater to
produce hot water and they won’t be able to get it at
very low flow rates (see “Is a Tankless Heater Right for
the Job?”).
In this article, I’ll discuss condensing storage heaters
and how they’re installed. Since natural gas is the
primary fuel in our region, I’ll be describing gas-fired
models, many of which can be field-converted for propane.
How They Work
In several respects, a condensing storage heater is like a
conventional model. Both burn gas, have exhaust flues, and
store hot water in an insulated tank. But a condensing heater
is much more efficient because of how heat is transferred to
the water.
In a conventional heater, the fuel is burned in an open
chamber, and hot combustion gas rises through a flue in the
center of the tank. A lot of this heat is transferred to the
water in the storage tank, but a good portion exits through the
vent pipe and is wasted.
In a condensing heater, a draft-inducing fan pushes air and
fuel into a sealed combustion chamber inside the tank
(see Figure 1). As the fuel burns, combustion
gas is exhausted through a secondary heat exchanger — a
coiled steel tube submerged inside the tank. The combustion
chamber and heat exchanger have large surface areas to maximize
heat transfer to the water. So much heat is transferred that
the combustion gases cool to the point where the water vapor in
the exhaust stream condenses, releasing its latent heat, which
is also transferred to the stored water. By the time the
exhaust gas leaves the heater, it’s cool enough to be
safely vented through inexpensive plastic plumbing pipe. (Each
manufacturer accepts different kinds of pipe; options include
specified types of PVC, CPVC and ABS. All are far less
expensive than stainless steel.)
Figure 1. A cutaway drawing of a Vertex
heater (above) shows the combustion chamber and secondary heat
exchanger coil inside the tank. In the Phoenix model at right,
the combustion chamber and secondary heat exchanger are located
in the upper part of the tank, with a second heat exchanger for
a solar thermal collector below.
The thermal efficiency (TE) of a condensing storage heater is
quite high, typically between 90 and 96 percent. (For an
explanation of thermal efficiency standards, see “Making
Sense of Gas Water-Heater Ratings.”) Standby losses are
low because the storage tanks are covered with thick foam
insulation — plus these units all have electronic
ignition, so there is no standing pilot.
Heating Capacity
Most people think of storage heaters in terms of tank and
burner size — as in a 40-gallon 40,000-Btu heater (see
chart). The Btu rating is a measure of fuel input to the
burner; output is measured in gallons of water heated per hour
to a particular temperature rise. The condensing heaters we
install have an input range from 76,000 Btu all the way to
199,000 Btu. (By comparison, the typical tankless model we
install is rated at 199,000 Btu.)
Recovery. The recovery rate tells how fast the heater
can replenish hot water as it is drawn from the tank. Recovery
is measured in gallons per hour at a 90°F
temperature rise; it’s a function of the burner size (Btu
input) and heat-transfer efficiency.
First-hour-rating. The number that we look at when
sizing a storage heater is the first-hour-rating (FHR) —
the amount of water it can provide in one hour at a
90°F temperature rise. FHR is a function of the size
of the heater’s tank and the recovery rate. The tank
factors in because it’s a reservoir of heated water, most
of which is considered to be available for immediate use. The
FHR is equal to the recovery rate plus 70 percent of the tank
size.
Installation
Condensing heaters have the same footprint as conventional
water heaters, so they work well for replacement jobs
(Figure 2). The units cost more than tankless
models, but because they’re easier to install in existing
construction, the higher equipment cost is often offset by
lower labor figures. A typical tankless heater wholesales for
about $950, and a 90-percent-efficient condensing storage model
for about $1,700.
Figure 2. This 50-gallon condensing water heater will
be installed in the space (right) previously occupied by a
40-gallon conventional storage model.
Many models can be connected to an existing 1/2-inch gas line
(Figure 3), though some of the larger units
require a 3/4-inch line. All condensing heaters require a
120-volt electrical circuit to run the fan and
electronics.
Figure 3. Condensing heaters can often connect to an
existing 1/2-inch gas line. The plumber extends the line (top)
to reach the inlet at the top of the heater. The air intake
(bottom left) — the PVC fitting with the screen inside
— is connected to a draft-inducing fan. Combustion gas
and condensate exit through a fitting near the bottom of the
tank (bottom right). The elbow connects to the flue and the
condensate hose runs to a drain.
Flue. The existing flue can’t be reused, but a
new plastic flue is inexpensive and easy to install. The draft
is fan-induced, so flue runs can be long — up to 128
equivalent feet, depending on the heater and whether the vent
is 2-, 3-, or 4-inch-diameter pipe. Makeup air can be drawn
from the room or piped directly to the heater from the
exterior. We try to terminate the flue at an inconspicuous
location on the outside, because it may emit a visible plume of
vapor and the fan may be audible there (Figure
4).
Figure 4. A plumber installs a section of flue pipe
(top), taking care to slope it so that condensate drains back
to the heater. With the particular heater shown here, the flue
can be ABS or PVC; in this case, it’s a combination of
the two (bottom left) because the plumbers ran out of ABS. The
flue passes out through the wall and terminates at a screened
fitting (bottom right).
Condensate. The water that condenses in the heat
exchanger and flue drains to a condensate trap and is fed
through a plastic hose to the nearest plumbing drain. The
condensate is acidic enough to erode concrete and metal, so it
has to be neutralized before discharge; this is done by running
it through a cartridge filled with crushed limestone or marble
(Figure 5). The cartridge needs to be checked
yearly and the stones topped off or replaced if they’ve
dissolved.
Figure 5. Condensate is acidic and should
be neutralized, which is done by running it through a cartridge
filled with marble chips or limestone. On this job (left), the
condensate is pumped into an air-gap fitting on a drain line.
At right, the condensate from a pair of heaters flows into a
floor drain (both heaters have neutralizers, though only one is
visible).
Base Models
Condensing heaters have been used commercially for about 15
years; they’re a proven technology. Because of the size
of their burners, the heaters from the four manufacturers
targeting the residential market are technically commercial
units. Most of them have electronic controls and diagnostic
sensors that can be accessed by a digital screen
(Figure 6).
Figure 6. In this installation, the heater and
condensate pump are plugged into a nearby electrical outlet
(left). A digital readout (right) allows the homeowner to
adjust the water temperature and the plumber to diagnose
problems.
Vertex and Premier. The least expensive condensing
heater is A.O. Smith’s Vertex. It’s sold in two
versions, both with 50-gallon tanks: a 76,000-Btu 90-percent-TE
unit and a 100,000-Btu 96-percent-TE unit. Both have
glass-lined tanks and taps that allow them to be used for
combination space-heating and water-heating applications. The
same heaters are also sold by State Water Heaters under the
Premier brand (Figure 7).
Figure 7. The Vertex (A.O. Smith) and Premier
Power-Vent (State Water Heaters) heaters are the same units
sold under different labels. Shown here is a
96-percent-efficient Vertex and a 90-percent-efficient Premier
Power-Vent model.
We like these heaters for retrofits because they’re easy
to install. They can often use existing gas lines, so
field-supplied materials are limited to piping and fittings
near the heater, the neutralizer cartridge, and flue pipe. The
heater itself is prewired; all we have to do is plug it into an
adjacent outlet. As a replacement unit, the installed cost of
one of these heaters is frequently less than the installed cost
of a comparable tankless model.
Figure 8. The Polaris (left) has a stainless steel
tank and a simple interface — indicator lights and a dial
for setting temperature. This Phoenix heater (right) provides
hot-water storage and boiler backup for a solar thermal
space-heating (radiant) and domestic hot-water
system.
Premium Units
The next step up is to a Polaris, made by American Water
Heaters, an A.O. Smith company, or a Phoenix, manufactured by
Heat Transfer Products (Figure 8). These
heaters have long-lasting stainless steel tanks and come in a
variety of tank and burner sizes, with inputs up to 199,000
Btu. Both brands include taps that allow them to be used for
combined space and water heating. Several of the Phoenix models
also contain heat exchangers that can be connected to solar
collectors for heating or preheating the water. Although we
have installed both brands, we have more experience with the
Phoenix because it’s readily available and better
supported in our area.
Jim Lunt co-owns The Lunt Marymor Co. in Emeryville,
Calif., with Leigh Marymor.