- Q.What is the maximum number
of 12-gauge wires permitted in 3/4-inch
conduit?
A.Master electrician Rex
Cauldwell responds: For practical purposes,
the maximum number of 12-gauge THHN conductors for
a 3/4-inch EMT conduit is nine.
The answer would be different for another type
of conduit (for example, ENT), or if the conductor
had a different insulation type or different
outside diameter. Although the NEC allows
up to 16 current-carrying THHN conductors in such a
conduit, it also requires that for any number of
conductors over three, you have to derate the
capacity of the conductor. The derating
isn’t significant until the number of
conductors exceeds nine. For 10 to 20 conductors,
12-gauge wire is derated down to 15 amps.