- Q.In an older house wired
with BX cable, can the original two-prong outlets be
upgraded to three-prong grounded outlets, provided
they’re properly bonded to the original
metallic boxes?
A.George
Flach, former chief electrical inspector
for New Orleans, responds: The answer depends
on what kind of BX cable you actually have. General
Electric’s original BX cable was
manufactured without a bonding strip — a
thin metal strip within the outer metallic jacket
that runs the length of the cable — or
bonding wire. Even if the cable is properly
fastened to the metal box, the spiral metal tape
jacket alone can’t be considered a
reliable equipment-grounding conductor. The only
way to upgrade a two-prong outlet to a three-prong
outlet with this type of wiring is by providing
GFCI protection, either with a GFCI breaker to
protect the entire circuit, or with a GFCI
receptacle at the junction box. Outlets on the same
branch circuit and those connected downstream of
the GFCI receptacle would also be protected.
(However, be sure to test the GFCI after
installation: If the test button doesn’t
trip, there’s no ground-fault protection.)
These receptacles must be clearly marked
“GFCI protected. No Equipment
Ground.”
Later versions of BX cable are equipped with a
small-gauge, uninsulated conductor; you may also
have AC (armored cable) with a bonding wire and
interlocked metal jacket. In either case, if the
cable is in good shape — and there is a
good connection between the outlet, the metallic
junction box, and the bonding wire — a
standard, properly installed three-prong outlet
would be grounded. An alternative would be to
install a GFCI receptacle or breaker, as above.
Before doing anything, though, I’d
remove the existing receptacle’s faceplate
and examine the wiring without disturbing it or
removing any receptacles. If the rubber insulation
on the branch circuit conductors is brittle and
falling off, don’t remove the existing
receptacle unless you intend to replace all of the
wiring, too.