New rules are complex but
flexible
The 2009 International Energy Conservation Code (IECC),
America’s national model energy code, was released in
January of this year. Typically, state and local code adoptions
lag several years behind the model code’s three-year
upgrade cycle — so a new model code usually isn’t
breaking news. But this time around, in response to federal
stimulus-package incentives, some states have already upgraded
to the new IECC. In Maryland, Maine, New Hampshire, Rhode
Island, and Illinois, the 2009 version will take effect as soon
as this October, with more states poised to follow suit.
The 2009 IECC is significantly more stringent than the 2006
version. It reduces a new home’s energy use 12 percent to
20 percent compared with levels set by the previous code. The
gains come from upgrades to a range of building elements:
increased wall, roof, and foundation insulation;
higher-performance windows; airtightness testing for ductwork
and building envelopes; high-efficacy lighting lamps; and more.
But the flexibility built into the new code’s basic
R-value and window efficiency tables — and relatively
sophisticated software-based “performance path”
— allows builders to comply while using strategies that
help keep construction costs under control.
Insulation levels. Required wall insulation R-values
have been bumped up in Zones 5 and 6 (see map) from R-19 to
R-20 — achievable with a high-density fiberglass batt in
a 2x6 wall. But there’s a “13 plus 5”
loophole that says you can also meet the requirement with an
R-13 high-density batt in a 2x4 wall, plus R-5 continuous
insulating sheathing (such as an inch of extruded polystyrene),
even though on paper the total R-value of that system would
only be R-18 (see charts).
Insulation R-values and window U-factors in the 2009 IECC are
based on this climate zone map, which is also used by Energy
Star and other model energy codes. On a county-by-county basis,
the map divides the country into eight major climate zones
based on heating and cooling degree-days, variations in solar
radiation, wet-bulb temperature, and other factors that affect
local weather conditions. (Zone 8 — not shown —
covers much of Alaska.)
Although the 2009 IECC has toughened the R-value
requirements for some climate zones (top), it also offers more
flexibility than earlier versions. A new U-factor chart
(bottom) can be used to calculate total heat loss — or
Total UA — through the building envelope (U-factor x area
= Total UA), allowing component R-values to be traded off
against each other.
While basic ceiling R-value requirements haven’t changed,
an exception has been added for cathedral ceilings that allows
reduced insulation in cases where roof framing will not
accommodate the full R-value batt thickness (this exception is
limited to just 500 square feet or 20 percent of total roof
area, whichever is less). There’s also an incentive for
raised-heel trusses, or “energy trusses.” If your
truss has a raised heel in zones where R-38 attic insulation is
required, you can cut back to R-30, in recognition of the
better performance achieved by insulation that covers the wall
plate at full thickness. (Attic hatches, by the way, have to be
insulated to the same level as the attic floor.)
The code now allows you to trade ceiling R-value off against
wall R-value. Using the “Total UA” method, you can
reduce wall insulation and increase roof insulation — or
vice versa — as long as the total calculated heat loss,
or “U,” through the whole house envelope remains
the same. To perform these whole-system calculations, there are
U-factor tables included in the code. In theory, you could use
these tables to calculate your Total UA numbers, but in
practice, you’ll want to use the DOE’s free
REScheck software, which is available in Windows desktop or
Web-based interactive form (energycodes.gov /rescheck/).
The wall R-value table also offers special allowances and
requirements for walls that aren’t wood-framed.
“Mass walls” — such as heavy log
construction, poured concrete, and concrete masonry —
have their own column in the table, reflecting the way mass
heat storage can improve a wall’s performance. Insulation
requirements for mass walls vary, however, depending on whether
the insulation is on the side facing the conditioned space or
on the side facing the outdoors: If you place insulation on the
inside, you need more of it, because the mass wall limits total
heat flow more effectively when the mass is interacting with
the occupied space.
And the insulating value of the massive material in the wall is
most significant in cooling climates: In Zone 1, for example,
where a wood frame wall would require R-13 cavity insulation, a
concrete wall needs just R-3 (exterior) or R-4 (interior)
continuous foam. In Zone 8 (found only in northern Alaska), by
contrast, a mass wall needs R-19 continuous insulation —
barely different from the R-21 required for batt or blown
insulation installed between studs in a wood wall.
Steel-framed walls and ceilings also have a column in the
tables. In this case, though, the R-value requirements are
higher, to reflect bypass losses from heat conduction through
the steel. And with steel framing, you need less insulation if
you provide it in the form of continuous insulated sheathing,
instead of as fiber insulation between studs or trusses.
Foundation insulation. The 2009 code adds a
requirement for slab edge insulation in Zone 4, the
southernmost of the northern zones. It’s not much, just
R-5 (an inch of rigid foam) — but you need an additional
R-5 if the slab is heated. Slab insulation has to extend 2 feet
down from the top of the slab in Zones 4 and 5, and 4 feet down
in Zones 6, 7, and 8. But any combination of horizontal and
vertical insulation qualifies — so you could run your
foam 2 feet down and then 2 feet sideways, either toward the
inside (under the slab) or to the outside (under the soil, as
long as there’s at least 10 inches of soil cover on top
of the insulation). The slab-edge insulation requirement can be
waived in termite country at the building official’s
discretion.
For basement insulation, things get a little more complicated.
The R-value table provides two numbers, one for continuous foam
insulation and another for cavity insulation installed between
studs in a framed-out basement wall. So in Zone 3, for example,
you can choose between R-13 batts between the studs and R-5
rigid foam applied over the concrete. Again, this disparity is
greater in the South; in northern Zones 6, 7, and 8, R-19 batts
between the studs are the equivalent of R-15 continuous
foam.
When basement walls are set into a slope and only partially
backfilled, you have to be careful. If the wall area is more
than half exposed, then the code treats it as an above-grade
wall. If it’s more than half buried, it’s a
basement wall.
Window requirements. In Zones 3 and 4, window rating
requirements have tightened. Zone 3 now requires a window
U-value of 0.50 (down from 0.65); in Zone 4, you need U-0.35
windows (down from 0.40). But this isn’t a minimum
— it’s a required average for the whole house. So,
for instance, you’ll meet the 0.50 requirement if half
your window area is rated U-0.40 and the other half is rated
U-0.60 (that’s by square footage of window, including
frame — not by window unit).
Airtightness testing. Air infiltration can make or
break a home’s energy performance. For the first time,
the 2009 code requires air leakage rates to be verified, by one
of two methods. Either you can get a point-by-point inspection
during construction of a long checklist of air-sealing measures
(similar in scope to the EPA Energy Star for Homes
program’s Thermal Bypass Checklist); or you can simply
get a blower-door test at the end of construction. For most
builders, the blower-door test is the simpler process.
Ductwork testing. Duct sealing can make a big
difference in home performance, particularly in cases where the
ducts run in an attic or vented crawlspace. In the new code,
all duct systems that extend outside the conditioned envelope
have to be pressure-tested to verify acceptable leakage. (Ducts
within a conditioned basement, conditioned attic, or interior
building chase don’t need to be tested, but they do have
to be air-sealed and inspected.) According to the DOE,
duct-sealing measures called for in the new code should result
in an 8 percent reduction in seasonal home energy use.
Lighting efficacy. The 2009 code has new — and
potentially confusing — lighting requirements: At least
50 percent of the lamps in permanent fixtures must be
high-efficacy (meaning a compact fluorescent bulb or something
better). Because this rule is stated in terms of
“lamps” — meaning bulbs — not fixtures
or wattage, a chandelier with 50 5-watt incandescent bulbs
would need to be offset by 50 compact fluorescent bulbs
elsewhere in the house. By the same token, an LED rope light
with 100 tiny high-performance bulbs — drawing less than
one watt each — could theoretically outweigh 99
incandescent bulbs at 200 watts apiece. In practice, your local
code official will have the final interpretation of this
rule.
Additions and renovations. Any substantial renovation
of a home — and any addition — has to meet the
energy code. There are two ways to achieve this: The whole
house can meet the code’s prescriptions, or you can
choose to evaluate just the renovated area by itself. So an
energy-efficient addition on an old, underperforming house
would meet the code; and a lower-performance addition to a
super-insulated, high-performance house could as well.
Sunrooms — one-story attached rooms that are mostly glass
— are a special case. The ceiling R-value requirements
and window U-factor limits are relaxed — provided that
the rooms are thermally isolated from the main house (including
doors that close) and separately zoned for heating and
cooling.
The software option. With so many variables to
balance, sticking to the prescriptive tables can be cumbersome.
Some builders may prefer to use the software-driven
“performance path,” which offers far more
flexibility — as long as the model predicts total house
energy consumption that’s equal to or better than a
code-compliant “baseline” home.
The software model’s output may reflect things that the
code tables don’t even mention — such as window
shading and reflective roofs in southern climates or passive
solar gain and heat-recovery ventilation in northern climates.
Unlike in past versions of the code, however, you can’t
trade off hvac efficiency against building-envelope
characteristics. A high-efficiency furnace or air conditioner,
for instance, won’t let you get away with reduced wall or
ceiling insulation.
The basic software tool for IECC compliance is DOE-2 (available
for free at doe2 .com). Other packages that offer the same
capabilities include EnergyGauge, REM/Design, and
REM/Rate.
Home labeling. Finally, for the first time, the code
now requires documentation of every new home’s
energy-conservation characteristics. The builder must post a
label that specifies window U-values, wall and ceiling
R-values, hvac efficiencies, and other key building
characteristics on the home’s electrical panel.
For a detailed walk-through of the requirements of the 2009
IECC, view the DOE’s 90-minute online training session at
jlconline.com/training. — Ted Cushman
Offcuts
An Illinois manufacturer accused of violating the FTC’s
“R-value Rule” has been fined $155,000. According
to the FTC, Meyer Enterprises claimed an R-value of 7.54 for
its Insul-Tarp underslab blanket insulation, when in fact the
product’s Rvalue is less than 2. A related case against
Enviromate, which claims that its Polycell cellulose insulation
has a chemical additive that doubles its actual R-value, was
settled without a fine. A third case, against Edward Sumpolec
and Energy Conservation Specialists — who sell
Thermalkool, an aluminum radiant barrier with a
“theoretical R-value of 53,” and Thermalcool, a
four-layer insulating ceramic coating that will “reduce
wall and roof temperatures by 50–95 degrees”
— is still in litigation.
A temporary moratorium on some building permit fees in June
saved Denver residents $85,773 and generated $6,283,957 in new
construction. Part of a program announced by Mayor John
Hickenlooper to spur the local economy, the two-week break
resulted in 1,234 new building permits — a three-fold
increase in daily activity compared with the previous month.
Projects that required a permit review, like new homes or
additions, weren’t included in the program.
After several months of continuous decline, the price for
materials used in single-family construction rose slightly in
May, according to the Bureau of Labor Statistics’ monthly
survey of wholesalers and manufacturers. The Producer Price
Index (PPI) had fallen 5.3 percent in the previous seven
months, but inched up 0.1 percent last month thanks to rising
energy and metals costs that offset continued declines in the
price of lumber, plywood, and drywall. Overall, plywood prices
are down 17 percent from a year ago; softwood lumber is down 36
percent; and gypsum products are down 22 percent.
The cost of photovoltaic electricity is plummeting. Thanks to
an oversupply in worldwide manufacturing capacity and lower
demand, prices for PV panels are expected to decline 43 percent
by the end of 2009, says the research firm New Energy Finance.
Now that the government has eliminated the $2,000 cap on the 30
percent solar-energy tax credit, a typical $32,000 4-kw solar
system that cost a California homeowner $23,000 last year after
state and federal incentives would — according to these
predictions — cost less than $12,000 this year.
About 9,000 DeWalt framing nailers have been recalled because
of possibly defective bump-trigger mechanisms that could cause
the gun to misfire or prevent the trigger lock-off from
functioning properly. The voluntary recall announced by DeWalt
and the CPSC applies to models D51850 (a round-head nailer) and
D51825 (the clipped-head version) sold from January to
September 2008. DeWalt advises nail-gun owners to stop using
the gun and contact the company at 877/437-7181 for a free
replacement bump-action trigger.
Since 2007, 84 Lumber has
closed 124 of its lumberyards and manufacturing plants while
cutting more than 5,000 employees — but on July 1, the
Pennsylvania-based company reopened its Houston facility.
“We believe we are starting to climb out of the housing
and general construction downturn, and we view Houston as one
of those markets that will be at the forefront of the
rebound,” said 84 Lumber vice president Frank Cicero in a
recent statement to the press.