A.Pat Huelman, cold climate
housing coordinator at the University of Minnesota,
responds: Whether or not the fireplace or exhaust fan will
cause problems depends on several factors. The most important
factors are the leakage characteristics of the house, the type
of combustion devices used for space and water heating, the
location and type of fireplace and chimney, and the presence of
other exhaust devices such as a clothes dryer, central vacuum,
or bath fans.
The quantity of combustion and dilution air needed by a
fireplace varies, depending on the type of fireplace, the type
of chimney, and the size and burning phase of the fire. The
amount might be as little as 100 or 200 cubic feet per minute
(cfm) at the startup or burn-down of a small fire in a
fireplace with glass doors, or as much as 800 cfm or more for a
large fire in an open fireplace.
If the house is very leaky, drawing that much air may cause
only a small negative pressure. But if the house is tighter,
pulling that much air may cause a very large negative pressure.
Although negative pressure can interfere with the combustion of
the fireplace, in many cases it simply limits the magnitude of
the fire, somewhat like a wood-burning stove with good air
control.
Negative pressure can certainly interfere with
atmospherically vented furnaces, boilers, or water heaters,
potentially causing spillage of flue gases. That’s why
you would be well advised to choose sealed-combustion
appliances. Also, excessive soil gas and/or garage gases could
be drawn into the home when the fireplace is in use.
Let’s assume for a minute that you want to limit the
negative pressure caused by the fireplace to 5 pascals. The
first table shows the size of combustion air opening needed,
assuming three levels of combustion and dilution air
requirements (see Chart A).
A. Makeup Air Required for a
Fireplace
| House Tightness | Blower Door (cfm @ 50 Pa) | Combustion Air Opening for: 200 cfm 500
cfm 800 cfm |
Very Tight
600
28 sq. in.
154 sq. in.
280 sq. in.
Pretty Tight
1,200
None
98 sq. in.
224 sq. in.
Kind of Tight
1,800
None
41 sq. in.
168 sq. in.
Typical
2,400
None
None
111 sq. in.
Loose
/td>
3,000
td>
None
None
54 sq. in.
Very Loose
3,600
None
None
None
If your house is very leaky, existing leaks may provide
adequate combustion and dilution air for your fireplace. If
your house is very tight, you will need a very large passive
air opening.
Now let’s focus on the 600-cfm cooktop exhaust fan. If
we know the cfm @ 50 pascals of the home using a blower door,
we can easily predict the negative pressure due to the
operation of this fan (Chart B).
B. Negative Pressure Caused by a 600-cfm
Exhaust Fan
Pa) | Predicted Negative
Pressure Due to 600-cfm Exhaust Fan |
Very Tight
600
50 pascals
Pretty Tight
1,200
17 pascals
Kind of Tight
1,800
9 pascals
Typical
2,400
6 pascals
Loose
3,000
4 pascals
Very Loose
3,600
3 pascals
A negative pressure of 3 or 4 pascals — which this
exhaust fan can cause, even in a very leaky house — can
pull the products of combustion down a fireplace chimney. This
is especially likely during the start-up or burn-down phases of
a fire. The simplest solution to this problem is never to use
the cooktop exhaust fan when the fireplace is being used.
However, remember that this same negative pressure could
cause spillage of combustion gases from an atmospherically
vented space or from water heating equipment. With this type of
exhaust device, sealed combustion equipment would be advised
for space and water heating.
If you decide that these approaches are impractical, you can
try to size a makeup air inlet for the cooktop exhaust fan.
Let’s assume a 20-foot smooth duct with three 90-degree
elbows and a screened hood. Let’s also assume that the
fireplace (or water heater) can tolerate 3 pascals. Assuming no
house leakage, you would need an opening of approximately 325
square inches, or the equivalent of a 20-inch diameter duct. If
we know the house leakage as measured by a blower door, we
could use Chart C to size the makeup air opening.
C. Makeup Air Required for a 600-cfm
Exhaust Fan
Very Tight
600
50 pascals
Pretty Tight
1,200
17 pascals
Kind of Tight
1,800
9 pascals
Typical
2,400
6 pascals
Loose
3,000
4 pascals
Very Loose
3,600
3 pascals
If the cooktop exhaust fan will be used while the fireplace
is in operation or with atmospherically vented space and water
heating, you should install a makeup air fan.
Now, if that isn’t complicated enough, there is one
last nagging issue. When the cooktop exhaust fan is used when
the fireplace is not, the makeup air often comes down the
fireplace chimney, commonly leading to homeowner complaints
about a sooty odor in the house. Unfortunately, it is very
difficult to seal the chimney completely.
In conclusion, a fireplace and a large cooktop exhaust fan
just don’t belong together in the modern house. The
fireplace by itself can be handled by selecting sealed
combustion equipment for space and water heating and
introducing the necessary combustion and dilution air,
especially for tighter homes and during the critical start-up
and burn-down phases. The cooktop exhaust fan can likewise be
handled by itself with proper selection of combustion equipment
and some provision for makeup air. It is very difficult or
impossible, though, to handle combustion and makeup air
requirements when a house has both a fireplace and a cooktop
exhaust fan. If both are an inextricable part of your plans, I
would recommend a different type of hearth product and a
kitchen cooktop or exhaust fan with much smaller cfm