Building a Reinforced Concrete Block Wall,
continued
On this job, the walls rose three stories and measured 37 feet
long by 49 feet high at the ridge (plus another 12 feet to the
chimney tops), with an 8-inch-thick core and a final thickness
(including the stone veneer) of about 16 inches. In addition to
several window and door openings, oversized fireplaces and
flues interrupted each gable to one side of center (Figure
3).
Figure 3. This massive
block wall rises three stories from the basement level where it
begins. LVL beams anchored into bond beams at each floor level
support the joists, while the wall studs are nonbearing. One of
the off-center fireplaces can be seen at lower
left.
Placing the Rebar
Just prior to grouting a lift, we set the vertical rebar,
allowing it to stand 18 to 24 inches higher than the last
course of block (Figure 4). This short projection provided
sufficient overlap between lifts while still allowing us to
lower the block over the rod without too much difficulty.
Tie-wire has no reinforcing effect in unifying separate bars; a
good overlap is all that's needed.
Figure 4. A simple
overlap in the vertical rebar is all that's needed to provide
continuity between lifts. The next course of block can then be
lowered over the projecting rods without too much
interference.
The vertical rebar schedule called for #5 bars set 16 inches
o.c., with four #6 bars set two per cell at the wall ends and
at either side of every window and door jamb. Additionally, we
used #3 stirrups at every other course, 16 inches apart
vertically, to reinforce the sides of all openings. Stirrups
cause individual rods to work together, increasing their
reinforcing effect (Figure 5).
Figure 5. Stirrups bent
from #3 rebar unify the effects of individual bars. Here, the
stirrups circle two vertical rod pairs at a wall end, ensuring
they will work in concert after the assembly is encased in
concrete.
To consolidate the grout in the cells, we used an Oztec rebar
shaker (Figure 6). This tool (800/533-9055;
www.oztec.com) has interchangeable heads
for various rebar sizes — #6 and #5 rebar, in our case
— and works extremely well. We found that it takes two
to run the shaker: one person to hold and operate the vibrator,
and another to control the head on the rebar. It's a great
tool: You can watch the grout puddle right into place. No more
hand-shaking rebar for this crew.
Figure 6. A rebar
shaker quickly consolidates the grout in the cells, ensuring
complete filling and embedment while saving time and
labor.
At each floor level and at the sloping rooflines, we
incorporated a bond beam, using KO block to create a continuous
horizontal form (Figure 7). The bond beam contained two #5
horizontal bars embedded in grout, one to each side of the
vertical rod. We carried the bond beam around the chimneys,
front and back, thus ringing them with rebar (Figure 8).
Figure 7. The walls
between cells in standard 8-inch blocks are kerfed half-height
with a masonry blade to create knockout (KO) panels. A course
of KO block allows rebar to be completely embedded in grout to
form a bond beam.
Figure 8. The chimney
flue interrupts the bond beam running through the block wall at
each floor level. To ensure the continuity of the load path,
the bond beam encircles the flue.