Back in 2006, I took on an unusual chimney-repair job in
Chestnut Hill, a well-to-do urban neighborhood on the outskirts
of Boston. When I first met with the new owner, he called the
1929 brick home's four decoratively corbeled chimneys its
"crown jewels." Certainly, viewed from the ground, they were
impressive. The two largest measured 9 feet by 3 feet 6 inches
in plan and towered 22 feet above the roof line. The two
smaller ones were 4 feet square and stood 14 feet above the
roof.
Inspection and Demolition
I was hired to inspect the chimneys for structural integrity
and conduct any necessary repairs. Indoors, the fireplaces
showed significant deterioration. Firebrick hadn't been used to
build the fireboxes, and water had infiltrated all the way down
each chimney, carrying leached salts that had crystallized and
expanded within the bricks, basically breaking them apart from
the inside out. In addition, the dampers had been installed too
low and too far back from the tops of the fireboxes, and the
smoke chambers were badly constructed. The flue paths weren't
directly vertical in any chimney, and the poorly built offsets
had compromised proper drafting. Sooty ceilings inside the home
proved that case.
It was a good bet that conditions were no better above the
roof, especially since the steep slope of the slate roof and
the massive height of the chimneys made them virtually
inaccessible to routine inspection or maintenance. To create a
safe working platform, we completely covered the roof with
scaffolding — another story in itself, not covered
here.
We found serious problems with all the chimneys, all due to
faulty construction (see Figure 1). The corbeled tops required
complete rebuilding. Vertical cracks had opened between the
corner "pilasters" and recessed faces on the biggest chimneys;
similar vertical cracks ran the full height of the two smaller
chimneys. Set back 1 1/2 inches, the recessed faces had not
been properly bonded in interlocking sequence with the corners.
Instead, the builders made continuous vertical joints, creating
serious weaknesses. Furthermore, the space that should have
existed between the clay flue liners and the brick was solidly
filled, eliminating the conventional allowance for flue
expansion.
Figure 1. Vertical cracks indicate a
chimney in trouble. A combination of water infiltration and
unrelieved thermal expansion of the flues caused the failure
(left). The view down the flue shows cracking and water seeping
in (right).
We ran a small video inspection camera down the flues and found
them crazed with stress cracks. The mortar had eroded out of
the abutting joints, a fire hazard for sure. We even found flue
tiles with corners broken due to rough handling during
construction, the gaps crudely patched with mortar. Those tiles
should never have been used. Making matters worse, the flues
were all undersized: Some were as much as 30 percent smaller
than necessary for proper drafting.
In short, the chimney tops had to be rebuilt and the flue tile
replaced; the vertical cracks had to be repaired and
reinforced; and the fireboxes needed rebuilding. Quite a list
of urgently needed repairs — and none of them
simple.
To begin we tore out the crumbling fireboxes, controlling the
clouds of demolition dust with a powerful exhaust fan at the
top of the chimney. Next we tackled the chimneys — but
not before tracing the corbels' profiles onto pieces of plywood
and taking photos, so that later we could rebuild them
according to their original design (Figure 2). Then we tore
down the top 4-plus feet of each stack, using small rotary
hammers to remove the brick below the corbeling.
Figure 2. Plywood templates and
photography will provide a visual record of the original
corbeling when the chimneys are rebuilt.
At this level, the quality of the original construction was
sufficient to rebuild upon — but not without
reinforcement to ensure strong structural chimney
corners.
Retrofit Anchors
We relied on a proprietary system called the Cintec Anchor
(Cintec, 800/363-6066,
www.cintec.com). The anchor
is a perforated stainless-steel tube encased in a fabric sock
(Figure 3); it comes in various lengths and diameters depending
on the application. When inserted into a cored hole in the
masonry and pressure-injected with a fluid grout, it creates an
extremely strong mechanical bond across the bricks. The sock
prevents the grout from entering any deep fissures that
intersect the coring. The anchors we used were 1/2 inch in
diameter and 22 inches long, and cost $7 apiece.
Figure 3. Reinforcing anchors presoak
before installation in the masonry. The anchors — hollow,
perforated stainless steel tubes in a fabric sock — come
in a variety of sizes; the ones shown are 1/2 inch in diameter
and 22 inches long.
Diamond Coring
To guide the 3/4-inch-diameter coring bit at the chimney
corners, I devised a jig of threaded steel pipe fittings and
lumber (Figure 4). After bottoming out with a short bit, we
removed the jig and let the hole itself guide a longer bit,
coring to a finished depth of 26 inches. We cored holes across
the pilaster corners at 3 feet on-center vertically, offsetting
them 8 inches from adjacent sides. In preparation for the
anchors, we blew each hole clean with pressurized air.
Figure 4. A short 3/4-inch diamond coring
bit, guided by a site-made jig, makes the initial hole for the
anchors (top). A long-shank coring bit (bottom) completes the
26-inch-deep holes, providing sufficient depth for the anchors
and a finishing masonry core plug.
Grouting
Cintec grout comes in 56-pound bags and is added to about 1 1/4
gallons of clean cold water. After it's mixed thoroughly with
an electric paddle, you let it stand for about five minutes,
while it thickens a bit. Then you mix in just enough water to
bring it to a smooth, creamy texture, ready for the pressure
pot and injection. The pressure pot is identical to that used
for airless spraying, except that the outlet must be modified
to accept a 1/2-inch hose adapter and up to 12 feet of
reinforced hose equipped with a quarter-turn ball valve. A
special mastic nozzle is provided, which you trim to fit the
anchor's injection tube.
With the grout in the pot and the pot pressurized to about 30
psi, we checked the flow for continuity and sufficient
pressure. To install an anchor, you fit the nozzle on the
anchor, insert it in the bore hole — taking care not to
tear the sock — and pump in the grout until the "grout
milk" stops flowing out of the hole. Rotating the anchor during
filling ensures that it's centered in the bore. We recessed the
anchors about 4 inches from the surface and plugged the bore
holes with a length of the cored material (Figure 5).
Figure 5. The anchor, fitted with its
proprietary mastic injection nozzle, is gently inserted into
the cored hole. Grout is pressure-injected until the "grout
milk" stops flowing from the site (top). The grout is delivered
from a conventional pressure pot at a relatively low psi
(bottom left). The author saved coring plugs to protect and
disguise the anchor holes after grouting (bottom
right).
At the top level — the point to which we'd demolished the
chimney — there was no practical way to introduce anchors
close to the surface. Instead, we cored down vertically, about
6 inches, at every corner (Figure 6) and grouted in custom-bent
stainless-steel straps to create a strong mechanical connection
between the corners and the inset face brick.
Figure 6. At the top of the completed
tear-down level, the author cores down vertically to install
stainless-steel reinforcing straps. A wet vacuum prevents the
slurry from staining the roof slates below (top left). The
straps are site-bent, with 4-inch drop legs, to suit each
location (top right). The strap holes are grouted in, while the
straps themselves are embedded in the following course of
mortar and brick (bottom).
Rebuilding the Chimney Tops
Following the profiles of the plywood templates we'd made
before demolition, we rebuilt the chimney corbels. This time,
we took care to use an interlocking layup at all corners
(Figure 7). We used concrete partition block to build the
chimney core. Corrugated stainless brick ties inserted at each
course provided mechanical reinforcement between the core and
the brick facing. No ties had been used in the original work,
another reason for its failure.
Figure 7. The author uses stainless-steel
corrugated wall-ties (about $1 each) and a layup that ensures
staggered bonding between bricks. The original work omitted
both of these reinforcing precautions.
To prevent future erosion, we installed custom-formed
lead-coated copper over the new concrete caps.
It's also worth noting that the Stiles and Hart Brick Co.
(800/320-8700,
www.stilesandhart.com)
in Bridgewater, Mass., took great pains in working with us to
custom-make new bricks that matched the originals. These were
oversized and without frogs (indentations on one side). The
result was a seamless union between the old and new work.
Custom bricks may sound like an expensive option, but in fact
the difference was only 20 cents per brick — about $1
each for the custom variety compared with 80 cents apiece for
stock.
Flues and Fireboxes
Before rebuilding the fireboxes, we had to reline the flues.
This part of the job requires specialized equipment and
materials, so we subbed it out to a contractor —
Bergquist Masonry of Temple, N.H. — certified in the
Ahrens two-part flue relining system (Ahrens Chimney Technique,
www.ahrenschimney.com).
Basically, the method involves breaking out the existing
ceramic flue tile from the inside by smashing it with a heavy
steel plate spinning at the end of an extendable drill shaft.
Smashing is effective as long as there's a gap between the flue
and the brick; solidly bonded tile is chipped away with an air
hammer fitted with a chisel on a long shaft. The work is done
from the top down. To remove the tile in flue offsets, side
openings are created.
Once the old tile is out of the way, relining begins. First, a
self-centering, cylindrical "bell" is drawn up the chimney's
interior through a proprietary masonry mix introduced from
above (Figure 8). The bell forces the mix against the
surrounding brick, forming a round (or oval) flue while filling
and sealing all voids and fissures along the way. The mix's
recognized insulating value is equal to 5 inches of brick per 1
1/2 inches of mix. Insulation minimizes creosote condensation
and flue expansion and contraction, and allows zero-clearance
contact between the chimney and combustible framing. (In older
construction, the framing is often found to be hard up against
the bricks.)
Figure 8. The Ahrens chimney relining
process involves drawing a bell-shaped flue-forming device up
through a masonry mix that's added by the bucketfulfrom above.
An offset wheel, visible at the end of the 2-inch-pipe, keeps
the bell centered in the chase.
Next, a thin lining coat is applied to seal the surface against
moisture and the acid produced by combustion gases. The final
result is a properly sized crack-free flue with good flow and
sufficient insulating qualities to control expansion
stresses.
Smooth Smoke Chamber
The smoke chamber is that transitional area between the firebox
and the flue, typically formed by corbeled masonry. When
damaged or improperly built, it can be a major source of house
fires.
The smoke chamber must be properly sized and its inner surface
parged smooth with insulating refractory mortar. (It's rare to
find any parging of the smoke chamber in older work.) With the
forward-sloping back walls of the fireboxes and the dampers
removed, we could stand inside the chambers and take care of
this critical job. We used another Ahrens product, Chamber-Tech
(www.ahrenfire.com), a
lining mix that sticks to just about anything. We made a ball
of it in our hands, slapped it on the brick, and troweled it
dead-smooth, rounding the corners and tapering the chamber to
transition to the new flue liner above.
To complete the work, we rebuilt the fireboxes and installed
new dampers. Although the flues and chambers were now properly
sized, the owner wanted a fail-safe system. So at the top of
each chimney we installed Exhausto fans (800/255-2923,
www.chimneyfans.com),
which cost about $1,000 each, draw 3 to 4 amps in operation,
and ensure perfect drafting.
With repair costs in the low six figures, these chimneys aren't
called the crown jewels for nothing. Nonetheless, they're now
better than new and will last a long, long time.
Mike DeBlasio is a masonry contractor in
Littleton, Mass.