A.Dave Yates, a plumbing
contractor in York, Pa., responds: Your home's
incoming municipal water line contains a backflow
preventer (BFP) or a pressure-reducing valve (PRV)
or both; either can lead to this problem. As cold
water is heated, it expands and must have somewhere
to "grow." Before BFPs or PRVs were required on
incoming water service lines, this thermal
expansion could be absorbed by the municipal water
system. However, now that most homes are closed
systems (water can enter, but can't return to the
street), there's no place for this expansion to go.
That's what killed your first water heater.
Your installer diagnosed your problem but may
not have installed a large enough expansion tank to
correct it. Residential expansion tanks start at
2.1-gallon capacity and go up from there.
Regardless of the size, Federal Department of
Transportation regulations limit the air charge in
a thermal expansion tank to 40 psi for shipping.
But if your home's water pressure is 80 psi, the
installer needs to adjust the air charge to match
final delivery pressure; if he doesn't, you will
lose half the tank's capacity as it takes on the
added 40 psi.
Even a 2.1-gallon expansion tank that's been
properly charged to 80 psi, though, can be
inadequate for a 40-gallon water heater. Here's
why:
A 40-gallon water heater can be subject to as
much as 1 gallon of thermal expansion (the exact
amount depends on inlet and storage temperature
range). But by applying Boyle's law (which states
that volume at a constant temperature is inversely
proportional to pressure, or P1 x V1 = P2 x V2), we
find that a 2.1-gallon thermal-expansion tank is
undersized even with the correct air charge of 80
psi. For example, when P1 = 80 and V1 = 2.1, if V2
= 1 then P2 will equal 168; this is why your
150-psi T&P relief valve is leaking
periodically.
Substitute 1.1 for V1 (if the plumber fails to
adjust the tank's air pressure upward) and .35 for
V2 (the volume left in the pressure tank if you get
another 3/4 gallon of thermal expansion), and you
could see a potential expansion tank pressure of
more than 250 psi. But with a 4.5-gallon expansion
tank — the next, larger size of
residential thermal-expansion tank — the
water in your system will have plenty of room to
expand without blowing your T&P relief valve
or ruining your water heater.
By the way, water pressures in municipal water
systems seldom remain constant; they tend to spike
at night as system-wide usage drops off. Those
spikes in pressure are then trapped within your
home's plumbing system, which will increase the
demands on the thermal-expansion tank for proper
protection. By spending $15 or $20 more for the
larger thermal-expansion tank, you have purchased a
pretty cheap insurance policy for your hot-water
heater.