First Time Out With ICFs
For a problem-free job, brace thoroughly, add superplasticizer to the mix, and place the concrete in lifts
19 MIN READ
First Time Out With ICFs, continued Reinforcement. Polysteel’s specs call for a minimum rebar placement of #3 bar at 2 feet on-center, horizontally and vertically. They also say to consult local building codes, but they provide a reinforcement engineering table that tells you how much rebar to place for walls of any height or thickness in various soil types. It’s a lot more rebar than most contractors place, I’d bet. On our job we placed the bar 2 feet on-center as specified, but I went up from #4 to #5 bar, just to be conservative. The added cost was insignificant, but, according to the table, this change increased the strength of the wall considerably. We placed the bar as we stacked the forms (Figure 3). The vertical bars sit beside the stubs sticking out of the footings. Horizontal bars lie in metal chairs, or hammocks, that span the forms and keep the bars centered within the wall space. When you use the metal chairs, you don’t need to tie the horizontal and vertical bars together with wire.
Figure 3.Polysteel’s instruction manual includes a reinforcement table that specifies the rebar size and placement for any soil condition, wall height, and wall thickness. Wire saddles placed across the forms keep the bars centered in the concrete core section (left). If saddles aren’t used, the vertical and horizontal bars must be tied together with wire (right).
Window openings. There were two windows and a door in one of my basement spaces. Since Polysteel is designed for above-grade as well as basement walls, the company has given windows a lot of thought. They’re not hard to deal with: You just build a window buck of pressure-treated wood to the rough-opening dimensions and add bracing to hold them in place during the pour (Figure 4). The permanent attachment between buck and wall is provided by 1/2-inch lag screws, 4 inches long, which are driven through the wood into the form voids. When the concrete sets up around the lag screw threads, the whole assembly is firmly locked in place.
Figure 4.Window openings are created with simple site-built window bucks made from pressure-treated 2×10 stock. A slot between the two spaced 2x4s that serve as the bottom sill makes it possible to pour concrete into the forms below the window opening. Temporary wooden flanges help position the bucks (the inside flanges are not yet in place in this photo), while added exterior bracing keeps them plumb during the pour.
Bracing. Adequate bracing is a critical part of any concrete pour, and this is especially true of ICFs. Don’t try to get by with fewer braces than the instruction manual specifies. We shot 2x4s into the footings on both sides of the wall at the bottom and then made a sort of ladder built of 2x4s to lie along the top edge of the forms (Figure 5). These upper and lower frames are connected with vertical 2×4 members spaced about 8 or 10 feet apart, and we braced them to stakes driven into the ground with additional 2x4s.
Figure 5.Vertical 2×4 braces spaced about 8 feet on-center tie into a 2×4 “ladder” laid over the top of the forms to stiffen them. Diagonal braces run from the vertical braces back to the ground (top), and a working platform tied into the bracing system provides easy access to the tops of the forms (bottom). It’s important to use at least the minimum bracing specified in the manual.
We also attached a working platform of 2x10s to the vertical braces at about half-wall height wherever access was at all difficult. It would be tempting to dispense with this working platform, but that would be a big mistake: It’s very helpful to have good, comfortable access to the whole top of the wall as you pour, so you can easily move the hose along and manipulate it.
The Pour
The waffle shape of the wall system conserves concrete: A Polysteel wall uses about 25% less concrete than a conventionally formed wall of the same nominal thickness. Polysteel’s handbook provides a formula for estimating concrete quantities based on the number of form blocks you use, and it seemed accurate — we had enough concrete and little waste. The handbook recommends a 3,000-psi mix at a 5-inch slump, with superplasticizer added at the job so the mix will flow easily into the forms and around the reinforcing.
To reduce stress on the forms, it’s important to pour in 1-foot to 2-foot lifts, at a total rate of about 4 vertical feet per hour. The superplasticizer wears off quickly, and the concrete in each lift stiffens enough that the pressure will not build up too high as the pour progresses.
Pumps and hoses. The standard way to place concrete in foam forms is to pump it (Figure 6). A 4-inch hose won’t fit between the forms and work around the form ties and rebar, so Polysteel’s instructions say to use a reducer to adapt the pump hose from 4 inches down to 2 or 3 inches. This lets the hose reach all the way to the bottom of the forms, allowing you to gently deliver the concrete into the bottom of the form on the first lift, rather than dropping it from a height of 6 or 8 feet.
Figure 6.A concrete pump delivers a 3,000-psi mix using small aggregate, and the mix is treated with a superplasticizer (left). The author’s concrete sub did not use a 2- or 3-inch reducing adapter on the pump hose, which would have made the pour more manageable. Rapping the forms with a hammer and a block of wood during the pour helps consolidate the concrete and prevents the formation of voids and air pockets (right).
We did not use a hose adapter on our job, and the effect was noticeable. At the beginning we were dropping the concrete several feet, and at the bottom of the forms I later noticed some bulging — as much as 1/2 inch of convexity between vertical braces in a few places. Since there was no finish issue in our case, this wasn’t a big concern, but I did think to myself that we were approaching the strength limit of the forms. Compared to conventional methods, using foam forms takes a bit of a delicate touch — the bracing and the placing methods really matter, because there is not a lot of tolerance for carelessness.
We actually did have a couple of minor blowouts — nothing catastrophic, but enough to cause some yelling and running around. One happened when the guy who was directing the pour mixed up his signals with the concrete pump operator. Instead of stopping the pump, the operator kept the crete flowing, and very quickly we had a high mountain of concrete at one spot in the wall. Under the increased pressure, a splice in a cut form about a third of the way up the wall bulged out and threatened to give way. Fortunately, we were able to contain the damage by jamming a piece of plywood over the tender spot and shoving in some new 2×4 braces against the side of the trench. We had a similar problem partway up a low section of wall where there was relatively little pressure involved (Figure 7). In that instance, we hastily shoveled some backfill back into the trench and tamped it down to offset the pressure of the concrete.
Figure 7.Inadequate bracing at a spliced form and a too rapid pour in one area caused a section of form to bulge outward (left). The affected area was located partway up a low section of wall, so the damage was contained by tamping backfill against the bulging form (below).
In hindsight, I think it would be wise to create some sort of augmented through-ties at any location where the form’s strength is at all dubious. I would also make the plywood gussets stronger and thicker next time and brace them back more thoroughly. It’s best not to allow wishful thinking into the work at all. Next time, I’ll definitely use the adapter, even though it’s tiring to have to continually slide the business end of the hose into the forms and lift it out again as you progress around the walls.
Curing. When you use ICFs, you’re doing your concrete a huge favor. The insulation contains the warmth that the concrete creates as it sets, and it keeps the moisture from evaporating. The temperature stays more uniform across the entire concrete section, and the concrete cures moist. That decreases the internal stress that often forms within a mass of concrete as it dries and cools differentially from the outside in. As a result, the shrinkage cracks that form will tend to be fewer and smaller. Also, a moist cure adds significantly to the concrete’s final strength — it’s reasonable to estimate that concrete cured inside ICF forms would end up at least 25% stronger than concrete that is wet-cured for seven days, and perhaps double the strength of concrete that is exposed to air a day or two after the pour.
Capping off. As you finish the pour, you place anchor bolts into the wet concrete just as you would for a conventional wall. In a few days, when the concrete is hard enough, you apply a pressure-treated sill in the usual way, although the sill itself is wider. The added thickness of the forms means that a nominal 6-inch wall is actually 9 1/4 inches across, which makes for a nice fit with a 2×10 sill. A nominal 8-inch Polysteel wall gets a 2×12 treated-wood sill cap.
The portion of the foam form on the exterior surface that’s above grade, between the ground and the house, needs to be protected. We used a cementitious stucco called California Stucco, from Silpro (www.silpro.com). It comes dry in a sack, and you mix it with water on site. Polysteel’s literature says you can apply the stucco directly to the foam if you rough up the foam with a wire brush first, and it’s true — that’s what we did, and the stucco does adhere. But in the future I think I would use expanded galvanized-metal lath, because the stucco we applied has developed some fine cracking. Another option would be to screw pressure-treated wood to the steel furring strips in the foam, or to apply some kind of fiber-cement sheet material.
Would I Do It Again?
When the forming and pouring were all done, and we stepped back to assess the results, my crew and I were impressed. I’ve got a crew of the usual cynical home-building types — each of my guys has been doing this kind of work for 25 or 30 years. And everybody, myself included, felt that this system was worth the effort and lived up to its promise.
I’m still not sure how the cost of this job would compare to the cost of bringing in a regular poured-wall subcontractor. There were a lot of wild cards in this particular project, including the unusual wall heights and my desire to protect the site. And as I mentioned, this was not the kind of job where I needed to work up precise bid figures or compare all the alternatives. This customer was ready to pay for quality.
But when I do figure up all the costs, I won’t be surprised if I find that this way was actually cheaper as well as better. I avoided the separate cost of insulating, and I avoided having to bear the cost of a specialty contractor’s markup and the cost of any delays caused by working around his schedule. The well-insulated basement space saves energy for the homeowner and is also more comfortable and livable than the usual basement.
In addition, by including a generous amount of steel reinforcement and by curing the concrete under ideal conditions, we’ve built what I am convinced is a very strong and durable wall.
I’ll be using ICFs on my next basement, even though I’ll be working at the opposite end of the market, building a small, bare-bones house with a tight budget. Even for a client who is by no means a moneybags, I think this system is worthwhile.
Malcolm Meldahl is a design-build contractor in Truro, Mass.
Malcolm Meldahl
Malcolm Meldahl is a builder and designer in Truro, Mass.