Structural wood panels fastened to a stick-framed wall add
stiffness and strength. That's the principle behind braced-wall
requirements in the International Residential Code (IRC), and
the principle underlying engineered shear wall design in the
International Building Code (IBC) and in engineering standards
such as the American Society of Civil Engineers standard
ASCE-7.
So if one layer of plywood or OSB on a framed wall is good,
would two layers be better? That's the question considered
recently by subscribers to the Structural Engineers Association
mail list at
www.seaint.org. Although the case in point related to seismic
issues, not wind resistance, the discussion offers lessons for
builders in high-wind country too.
The problem was raised by Long Beach, California, engineer
Charles Laines. In a posting, Laines wrote, "Contractor
'forgot' the interior layer of plywood in a shear wall spec'd
for sheathing on both sides. Wants to put double layer on the
outside since the interior has been finished. I cannot find any
restrictions in the codes."
Several engineers responded skeptically to the idea of
doubling up "shear panel" on one side of the wall, instead of
on the inside and outside faces. One engineer's gut reaction:
"I can’t imagine that two layers of sheathing of the
same side of the wall would accomplish anything other than
tearing the studs up." But Tom Skaggs, Manager of Product
Evaluation at APA - The Engineered Wood Association, chimed in
to note that there is some precedent for the proposed idea. "We
did testing on double layered singled sided diaphragms," wrote
Skaggs. The concept was a retrofit of an existing roof
diaphragm with a second layer of panels, fastened with 14 gauge
staples. Panel edges were staggered so that edge nailing would
miss the framing, Skaggs noted, and "results were favorable."
Download "Research Report 138" from the
APA Web site.
Coastal Connection contacted Tom Skaggs to ask if the idea
of adding panels to the outside of a structure might be valid
in high-wind situations — for example, as a wall
retrofit in Florida or elsewhere on the Atlantic or Gulf
coasts, when existing siding was being replaced anyway. After
consulting with several other APA engineers, Skaggs got back to
us with some comments. "Tests have shown that it can work," he
noted, and the building code states that "shear walls are
permitted to be calculated by principles of mechanics without
limitations." But field installation details are significant,
Skaggs warned: "The biggest concern is splitting of the shear
wall boundaries. And it’s extremely difficult to
assess splitting in a non destructive fashion."
Skaggs also passed along a more detailed response from APA
Help Desk engineers, who noted two building code references:
"2006 International Building Code, Section 2305.3.9, Summing
shear capacities. The shear values for shear panels of
different capacities applied to the same side of the wall are
not cumulative except as allowed in Table 2306.4.1."
That table makes no mention of two layers of sheathing on a
single side of the wall, the Help Desk said. But when it comes
to two-faced shear walls, the code reads, "The shear values for
material of the same type and capacity applied to both faces of
the same wall are cumulative. Where the material capacities are
not equal, the allowable shear shall be either two times the
smaller shear capacity or the capacity of the stronger side,
whichever is greater."
Can these principles be extended to shear walls with double
sheathing layers? The Help Desk offered a cautious "yes":
"Even though two layer shear walls aren't directly
addressed in the code, there is no technical reason to
prohibit their use provided that the calculated design
capacities can take the calculated loads and a load path is
provided. The calculated design capacities could be
developed using the principles established in the high
shear load diaphragm noted above. The capacity of the wall
hold-downs should be given careful consideration; their
ability to resist overturning may be the limiting
factor".
To our knowledge, this particular system has never been
tested either monotonically (static) or cyclically. APA
Engineers see no reason why this system could not be used in
ways similar to use of a double-sided shear wall or a
double-sheathed diaphragm (as discussed in APA Report 138)
if:
1.) minimum fastener penetration into the framing is met
2.) panel vertical edges are staggered to minimize lumber
splitting
3.) consideration is given to top and bottom plate
fastening
4.) overturning, including hold down and bottom plate crushing,
is studied
One engineer, formerly with APA, has suggested using 50% of the
shear capacity of the top layer as additional capacity. It
would appear, that this approach would be a conservative
alternative. However, if care is taken in fastening the top
layer, this approach might be too conservative.
Is it a good idea? Maybe. But as Tom Skaggs remarks, "The
shear wall capacity of the panels are limited by nail bending,
and not panel shearing through the thickness. So, perhaps a
more cost effective solution is to just add fasteners into the
existing panels."