Venting Gas Fireplaces -
Continued
Water heaters have slightly less stringent efficiency
standards, so most of them still use the old draft-hood
technology and rely on natural convection to pull air into the
combustion chamber. The draft hoods let dilution air enter the
flue, which provides some drying (but at the cost of lower
total efficiency).
One cubic foot of natural gas supplies about 1,000 Btus of
energy. Fan-assisted units need about 15 cu.ft. of air to fully
combust that 1 cu.ft. of fuel, producing about 16 cu.ft. of
cool, damp exhaust. Draft-hood units require an additional 14
or 15 cu.ft. of dilution air for each 1 cu.ft. of fuel
consumed, producing roughly 30 cu.ft. of relatively drier
exhaust products for the flue to handle. (The ratios are
slightly different for propane, but the principle is the
same.)
This difference between fan-assist and draft-hood performance
has an effect on venting requirements. Because a draft-hood
appliance creates a large volume of exhaust, it needs a taller
or larger-diameter vent than a fan-assisted unit of the same
Btu rating. Oversizing, however, isn't a problem: A vent
serving a draft-hood unit can only be too small, not too
large.
A vent that serves a fan-assisted appliance, on the other
hand, can be too small or too large. Because its exhaust
gas is relatively cool and damp, the fan-assisted unit won't
warm the vent quickly enough to prevent damaging condensation
(and with fan-assisted equipment, there's no drying airflow
through the system when the unit's not running). So for each
vent configuration listed (height, lateral run, and diameter),
the tables show both a minimum and maximum allowable Btu rating
for fan-assisted equipment ("fan min." and "fan max."). For
draft-hood equipment, the tables show only the largest
equipment permitted on the vent ("nat max.") -- there is no
minimum. For two appliances "common-vented" on the same flue,
the tables provide a complex range of options depending on
whether the setup involves two "fan" appliances, two "nat"
appliances, or one of each.
Vent materials. The sizing
tables also must account for the different behavior of
different vent materials. Masonry chimneys take a long time to
heat up and are prone to condensation, so they can serve only a
very restricted range of appliance sizes (and seldom if ever
can handle a fan-assisted unit by itself). Chimneys on outside
walls are especially problematic and should generally be
relined with a listed metal liner for use with gas. B vent (the
standardized, listed double-wall insulated vent pipe material)
is by far preferable to masonry and permits a much wider range
of equipment sizes. B vents and chimneys each get their own
sizing table in the code.
Single-wall metal vent connectors, though still in wide use as
the least expensive choice, also limit both the minimum and
maximum sizes of equipment permitted on a given size of vent.
They lose heat more quickly than B vent connectors, weakening
the draft and raising the risk of condensation wherever they're
used. They're also less fire safe: They require a 6-inch
clearance from combustibles, compared to 1 inch for B vent, and
they can't run in a concealed space or through an unheated
attic or crawlspace. In general, single-wall vent connectors
are best avoided, in spite of their lower cost. Still, sizing
tables are provided for single-wall vent connectors, either
with masonry chimneys or with B vents.
Using the Sizing Tables
In matching equipment to vents, the pitfalls are many. Too
small a vent diameter, and you won't have enough draft; too
big, and you might get condensation. Too long a horizontal
connector, too short a vertical vent, too low a connection to
the vent, too many elbows, too small a vent diameter, or all of
the above, and the vent won't draw. A setup that will work with
B vent might not work with a masonry chimney; one that works
with double-wall insulated vent connectors might not work with
single-wall vent connectors.
The sizing tables reflect all of that complexity, with more
than ten different tables that apply to different situations.
We're not going to teach everybody how to use the sizing tables
like a pro with this article. That takes training and practice,
and even experienced professionals find it easier to use a
computer. But we'll give you a few examples just to clarify the
idea.
A single appliance. Let's
start with the simplest case: a single appliance connected
directly to a vent or chimney. You could connect it to a B vent
with a B vent connector, to a B vent with a single-wall
connector, to a masonry chimney with a B vent connector, or to
a masonry chimney with a single-wall connector. The tables show
you how big an appliance you can use in each case, for various
heights, horizontal runs, and diameters of vents.
Figure 3 shows just a small section cut from the appropriate
sizing table for each of those four options. We're showing what
the table tells you for either a 10-foot or a 15-foot vent
rise, with a range of horizontal runs. If the rise falls
between 10 and 15, you're allowed to interpolate -- but let's
not go there.
Figure 3.Vent height, vent lateral run, vent
diameter, and vent material all must be factored into the
sizing match between an appliance and its vent system. In
general, tall B vents with no lateral runs offer the greatest
freedom of choice for appliance size. Lateral runs, elbows, and
single-wall vent pipe sharply degrade vent performance and
restrict appliance selection. In the example of a 10-foot vent
height with a 5-foot lateral run (circled in table), a 4-inch B
vent and B vent connector can serve any fan-assisted appliance
larger than 32,000 Btu/hr and smaller than 113,000 Btu/hr.
Increasing the vent diameter to 6 inches raises the minimum to
52,000 Btu/hr and the maximum to 280,000 Btu/hr. But using a
single-wall vent connector shrinks the maximum to 111,000
Btu/hr while raising the minimum to 76,000 Btu/hr. Fan-assisted
appliances are ruled out for masonry chimneys regardless of
connector type.