by Ted
Cushman
According to the latest U.S. Census, more than 150 million
Americans live in coastal counties of the United States (including
the East and West Coasts, the Gulf Coast, and the Great Lakes
coastlines) — many of them in areas that are at risk of
flooding either from heavy rainstorms or from hurricane storm
surges. As more people migrate to the coasts each year, that number
is predicted to grow.
Charlie Carll, Research Forest Products Technologist at the
U.S. Forest Products Laboratory, attaches temperature and humidity
sensors to the underside of a floor system at Musicians' Village in
the Lower 9th Ward of New Orleans. Researchers have begun a
year-long effort at the community to document the performance of
various insulation and air-sealing methods in raised floor
construction.
For new homes in these flood-prone areas, a pier foundation with an
elevated floor system is a well-established solution. In many flood
zones, it's the only option: to be eligible to participate in the
National Flood Insurance Program (NFIP), or to qualify for federal
aid in the event of a flood disaster, communities have to prohibit
closed foundations for any building built in the FEMA-designated V
zone (where there's a risk of storm-surge flooding accompanied by
waves 3 feet high or higher). Many localities go a step further,
requiring open foundations in the recently defined "Coastal A Zone"
as well (the zone subject to waves between 1.5 and 3 feet
high).
In the March/April 2008 issue of Coastal Contractor, we wrote that
elevated slabs on fill within a perimeter stemwall can work well in
a coastal A zone. But engineer Cathy Kaake, of the Southern Forest
Products Association, recently noted, "Most floodplain managers I
talk to are discouraging that type of foundation in that area."
Mississippi Emergency Management Association's Al Goodman, the
state coordinator for the NFIP, confirms that coastal counties are
not allowing elevated slabs on fill in the coastal A zone. It's not
that the 1.5-foot waves would damage the concrete foundation, he
says: "It'll hold up okay, but it will divert the waves and the
water against adjacent properties. That's why it's not
permitted."
In fact, Cathy Kaake reports, "That's why my house got flooded in
Katrina." After her house was built, builders had imported fill to
raise the elevations of nearby lots and build homes on slabs. When
the flood came, water that would have previously gone onto adjacent
areas flooded Kaake's property instead — the kind of event
that has happened often enough that regulators have begun to
restrict the use of fill in flood zones nationwide.
Elevated to the proper height, and built according to the specs
outlined in documents such as FEMA 55 (Coastal Construction Manual;
www.fema.gov/library/viewRecord.do?id=1671)
and FEMA 550 (Recommended Residential Construction for the Gulf
Coast; www.fema.gov/library/viewRecord.do?id=1853),
raised floors on pier foundations offer good flood resistance while
allowing floodwaters to wash harmlessly under a home without
impacting the neighbors. In regular A zones, where wave action is
not an issue, raised floors on an enclosed perimeter foundation or
on a filled slab are effective options. But an enclosed crawlspace
foundation is required to have "flood vents" to relieve water
pressure in the case of a flood.
Structure Meets
Climate
There is a hitch, however: in any climate — and especially in
the hot and humid Gulf Coast climate — raised floors can be a
building science headache. Whether a builder places the floor
system on pier supports or on a perimeter stemwall, he has to face
interrelated problems of air sealing, insulation, and moisture
protection that are neither easy nor cheap to solve. That's the
consideration that leads building science consultant Paul LaGrange
to say, "The best crawlspace is no crawlspace."
When he talks about crawlspace problems, LaGrange speaks from
experience. A longtime builder in South Louisiana, he now works as
a building science consultant who troubleshoots moisture and energy
problems. He also runs an insulation company that has insulated
scores of preexisting floor systems over crawlspaces. LaGrange has
personally spent more hours under low-to-the-ground floor systems
than he cares to remember. "We've done hundreds of them," he says.
"We were doing it years before Hurricane Katrina hit."
LaGrange notes there's a difference between the moisture
environment under a floor supported by open piers and the situation
within a fully enclosed crawlspace that has just a few air vents:
"Normally, the moisture content of the air and the ground are
higher under a fully enclosed stemwall-type application with vents
as opposed to an open-type crawlspace." The wide-open arrangement
is more common in South Louisiana, he observes. But both types of
foundation experience elevated moisture under the home (Figure
1).
Figure 1. Fully enclosed crawlspaces like this
one see more severe moisture conditions than open crawlspaces that
result when homes are supported by pier and beam systems, reports
building science consultant Paul LaGrange. In this example, air
conditioning ducts were already dripping condensation in early
spring of this year. In general, ducts should be kept out of
crawlspaces and placed within the conditioned living space wherever
possible.
Traditionally, raised floors in Louisiana were built without
insulation. But with the advent of air conditioning and the spread
of modern energy codes, many of those older floors have been
retrofitted with fiberglass insulation. Where the floor is not
insulated, LaGrange says, floors are cold in winter and warm in
summer. But when the floors have received fiberglass batts, the
frequent result can be moisture condensation at the underside of
the floor. Ineffective as an air barrier, the fiberglass allows
hot, moist air to penetrate and condense under the cool air
conditioned floor in summer.
"Fiberglass isn't the only problem, but it contributes to the
problem," explains LaGrange. Often the insulation has not been
installed in full contact with the subfloor; other times, it has
grown moist from condensation, gotten heavy, and fallen away from
the floor, leaving a gap (Figure 2). When he takes moisture-meter
readings of the subfloor where the fiberglass has fallen down,
LaGrange says, he finds higher wood moisture content than in areas
where the fiberglass is tight to the subfloor. "And you can
physically feel a difference in the fiberglass," he adds. "It's
more moist when it's not in full contact with the floor."
Figure 2. Fiberglass insulation installed
under elevated floors is typically unprotected and poorly
supported. At top, wire mesh has come loose and allowed insulation
to fall. In the middle photo, material held up by tacked-on furring
strips has become bunched and compressed. The drooping batts at
bottom were simply nailed to the subfloor in a few places with cap
nails. In all cases, the insulation's performance is degraded or
negated.
The typical result of all that moisture is trouble with flooring in
the occupied space — in particular, buckled wood strip
flooring or mildew under the carpets. In some cases, moisture
problems are more extensive: balloon-framed walls in older homes
may be open in some spots to the moist under-floor space, so that
moisture is drawn through the framing voids into many areas
throughout the house, causing uncomfortable conditions and mildew.
In severe cases, subflooring or flooring may be heavily attacked by
fungi (Figure 3).
Figure 3. Insulation that keeps the subfloor
area cool but allows moisture to penetrate exposes the floor to
potentially damaging condensation. Over time, the consequences may
progress from a small amount of mildew (left) to a major
infestation of wood-destroying fungus (right). Before badly damaged
wood is protected by more effective insulating material, it should
first be cleaned and treated by a capable mold remediation
contractor.
Possible
Prescriptions
For homeowners with these problems, LaGrange offers two possible
prescriptions: "Either apply rigid insulation board directly to the
underside of the floor joists, taping the seams and sealing the
penetrations; or apply spray-foam insulation into the joist
cavities, with vapor-retarder paint on the underside." The
rigid-foam alternative works well and is an attractive option for
do-it-yourselfers, says LaGrange: "If you have access to reasonably
priced labor, rigid foam is a great application. There is nothing
wrong with it, assuming you do it right and seal everything." (See
illustration, Figure 4.)
Figure 4. This ideal recommendation for
elevated floor insulation in the South Louisiana climate, devised
by building scientist Joseph Lstiburek (www.buildingscience.com),
calls for rigid-foam insulation under the floor frame as well as on
wall exteriors between the sheathing and the siding. With this
method, the insulation is almost completely continuous between the
floor system and the wall system, while most of the house's framing
is kept inboard of the insulation and air and vapor barrier,
subject to controlled interior conditions rather than exposed to
the stresses of the natural climate.
With spray-foam applications, LaGrange applies a skin of
vapor-retarding paint to the insulation after installing it. That's
because he uses an open-cell foam (Sealection 500 from Demilec,
www.sealection500.com)
that stops air movement but that, without the paint, might allow
too much vapor to diffuse in through the foam (Figure 5). Despite
its lower R-value per inch, LaGrange says, he prefers the open-cell
foam for its flexibility and strong adhesion: occasionally, he has
seen cracks open up between the more rigid, higher-density
varieties of foam and the floor joists, as the floor systems flex
and bend under foot traffic.
Figure 5. In a very damp crawlspace,
low-density open-cell foam may not protect structures from vapor
diffusion and moisture attack. The surface of the spray foam at far
left is glistening from vapor condensation. At left, rippled
reflections of the wood flooring in the occupied space above the
foam-insulated floor has cupped because of excessive moisture that
penetrated the insulation. In the recently begun research project
at Musicians' Village in New Orleans, scientists are trying to
learn the best way to prevent such moisture problems.
In Baton Rouge, La., insulation company Green Bean Insulation
(www.greenbeaninsulation.com)
has been plying the same trade as Paul LaGrange, using a
high-density R-5-per-inch open-cell foam (Figure 6). Along with its
flexibility and tenacious adhesion, Green Bean manager Mark Comarda
points out, the porous foam (www.apexfoam.com) has the advantage
that it is forgiving of bulk water leaks in the house above. "If
you had a leak on top, like in the bathroom or a hot water heater,
and that leak came down through the floor, it wouldn't penetrate a
closed-cell foam, because closed cell foam is a complete moisture
barrier. The water would just sit there between the foam and the
wood, and eventually it would rot out the wood." The open-cell
foam, explains Comarda, allows water spills to weep through and dry
out naturally — or at least declare their presence so that
the area can be opened up, dried, and repaired.
Figure 6. In this crawlspace, Green Bean
Insulation installers have insulated and air-sealed ductwork at the
same time as they insulated the floor system. The
1.2-pound-per-cubic-foot foam used here costs the same as
1/2-pound-per-cubic-foot material, says Green Bean's Mark Comarda,
but is less porous and has a higher R-value.
But the porous foam is still a highly effective air barrier. Many
of the older Baton Rouge homes he treats have no plywood subfloor,
Comarda says — just board strip flooring with many cracks and
gaps that allow airflow. That makes the houses leaky and cold in
winter, when temperatures can drop below freezing even in
Louisiana. "That's when we get the most calls," he observes. Spray
foam puts a stop to that source of discomfort. And after several
years in business, says Comarda, "Nobody has complained that it
doesn't work — not one person. We get an occasional call that
we missed a spot or something, and we have to go back and hit it.
But no complaints about the effectiveness of the product."
Foam is not a simple technology, however, and it takes expertise to
use properly. "Foam is finicky," says Paul LaGrange. "The
application depends on so many variables — humidity in the
air when you're spraying, the moisture content of the floor
assembly…. That's why we have one guy, our production
manager, who is always on site when they're spraying, watching the
guys recirculate the chemical, watching the temperature, recording
the ambient conditions and the condition of what we're spraying to.
It's his job to keep track of all those issues so if we do have a
problem, we can go back and analyze what happened."
And foam does best with a clean, dry substrate. After inspecting a
crawlspace, LaGrange says, he may have to advise a homeowner to
call in a mold remediation contractor to clean the floor system and
apply a nontoxic borate-based preservative treatment (in Louisiana,
only licensed contractors are allowed to do this type of work).
Sometimes, moisture-damaged materials have to be torn out and
replaced before foam can be sprayed.
When he insulates under a raised floor, LaGrange notes, he also
takes care to address ground moisture issues. If the floor is less
than about 4 feet above the ground, he covers the ground with a
10-mil plastic sheeting, weighted down with gravel. But first, in
some cases, it's necessary to raise the grade under the house.
"It's very common around here that the ground has subsided over the
years, and people have filled in their yard to compensate but have
not done anything about it under the footprint of the home. So the
area under the home becomes like a saucer that will hold water
— even with a regular rain, to say nothing of rising
floodwaters. Months after the hurricanes hit, it was nothing for me
to go crawl under a house and see water puddled under there." That
condition fosters rot as well as termites and mosquitoes — so
when he finds it, LaGrange places gravel fill beneath the building
to mound the ground up above the surrounding grade, before
installing the plastic sheeting.
Scientific Support
The field experience of contractors like Green Bean and Paul
LaGrange speaks to the effectiveness of the spray-foam solution.
But it's not the cheapest solution — and no one has ever gone
beyond informal experience to scientifically compare the
performance of high-density foam, low-density foam, rigid foam
board, and fiberglass in under-floor applications under controlled
conditions. At least, not until now: With support from the USDA
Forest Products Laboratory and funding from the Southern Forest
Products Association, in cooperation with the Louisiana State
University extension program, researchers are now setting out to
study all four insulation solutions in identical houses in New
Orleans.
The houses, built by Habitat for Humanity to house musicians
displaced by Hurricane Katrina, sit on pier foundations and were
originally insulated with fiberglass batts between the floor joists
(Figure 7). Now, researchers led by FPL scientist Sam Glass are
removing the fiberglass and installing moisture sensors and
thermometers in the floor frame cavities, as well as in the space
beneath the floors and in the yards next to the houses. They're
also placing temperature and moisture sensors in the house living
space to monitor indoor conditions. Then, contractors will install
four different insulation and vapor barrier systems under the floor
(Figure 8), and the scientists will use data-loggers and field
observations to record how the floor systems and the home interiors
behave for 12 months.
Figure 7. Musicians' Village, a community of
identically built Habitat for Humanity houses in New Orleans' 9th
Ward, is the site for a research project into insulation
performance in elevated homes. Existing fiberglass insulation,
although relatively carefully installed, is still of dubious value
in this application. Researchers plan to replace some of the
fiberglass with other insulation systems, and monitor the results
for a full year.
Figure 8. For research sponsored by LSU, FPL,
and SFPA, rigid insulation will be attached to the underside of
some Musicians' Village Habitat for Humanity homes. Band-joist
areas will be sealed and insulated with spray foam, and subfloors,
house interiors, locations under the house, and outdoor locations
away from the home footprint will all be instrumented so that
temperature and humidity conditions can be monitored as weather
changes, day by day and week by week, through a full 12-month
annual cycle.
The Musicians' Village research project will study the performance
of various types of spray-foam insulation, with and without an
additional layer of vapor barrier paint, side by side with a rigid
foam board insulation method and with the preexisting fiberglass
insulation originally installed in the homes' floor
systems.
Southern Forest Products Association engineer Cathy Kaake says her
organization is convinced of the flood-resistance advantages of
raised floor construction in low-lying areas. SFPA offers detailed
guidance on constructing the structural assemblies on its website
(www.raisedfloorliving.com).
But as Kaake admits, the moisture and energy details are not as
comprehensive as the structural details. "We put in the best
information we had at the time," she says. "But that's why we are
supporting the FPL and LSU research — we want to come up with
the best-practice solution. It's the number one question I get when
I go out and do seminars for engineers and builders and code
officials: ‘What is the best way to insulate? What is the
best way to control moisture?' And that is what we want to
answer."
Contributing editor Ted Cushman has been
covering residential building science and construction since
1993.